New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
APC 1375 UPS
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-0202:13 PM
APC 1375 UPS
I have an APC 1375 UPS. Ever since owning this device I have had the following issue. A power outage occurs and drains the battery. The unit shuts down. Power is restored. The unit recharges the internal battery but it does not turn back on. The only way to get the unit to turn back on is to disconnect it from the wall, access the internal battery, disconnect it for a minute or so and then reconnect the battery. As soon as you do, you can power up the unit and, it will show that the internal battery is fully charged and it will resume normal operation. Surely this device isn't designed to require that after each use. Can anyone advise me what's going on here?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-0304:22 AM
Connect the unit to a computer system running APC PCPE / PCSS Software. Are there options to select restart / resume upon AC restore?!?
There are also settings to define how many minutes left (remaining) before system shutdown.
The default is approximately 5 minutes so change it to 8-10 minutes. Simulate a lights out / grid down event by pulling the AC Mains cord from the wall.
Does the system operate correctly during at least ten minutes?!? If yes reconnect the AC Mains plug to the wall.
Does the unit continue to operate fine and displays its recharging the battery?!? All of this should also be viewed on the computer running APC PCPE / PCSS software.