Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

AP5201 KVM switch, USB not working

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • AP5201 KVM switch, USB not working
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

0 Likes
6
2553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

AP5201 KVM switch, USB not working

We recently put some new servers in our rack that only have USB inputs for the keyboard and mouse. When connected through USB, the keyboard and mouse do not respond. I have tried the following: PS2 to USB adapter with existing KVM cables, off brand USB KVM cable, APC USB KVM cable

In all cases, I have gone through server reboots to see if the issue was on the server side. I have also verified that other USB devices are recognized on the USB ports in question. Have also tried both front and back ports.

At this point I am thinking it is the KVM switch. Is it possible I need to do a firmware upgrade? If so, how do I tell what version of firmware is currently on the switch?

Any other thoughts or suggestions would be welcome.

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

0 Likes
0
2553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

Was there ever a resolution on this? As I appear to have the same issue. 

Connecting an AP5719 through an AP5201 using the AP5253 and have video but no mouse or keyboard. 

Keyboard on AP5719 works ok into AP5201 for OSD and hotkeys. 

USB mouse and keyboard plugged directly into Dell R330 server work fine. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

0 Likes
0
2553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

I'm bringing this one back from the dead.

Finally upgraded the firmware on the 5201 to v1.5.141 and still no luck with usb support. I get video when I wake up the server with another USB device, but the keyboard and mouse do not respond.

I tried connecting to a spare pc and rebooting (as you normally do with ps2 devices), but this did nothing.

The apc cable part number is AP5253. Why would only an APC usb cable work?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

0 Likes
0
2554
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

that cable is fine. i just meant that between the APC KVM and your server, the only cable you can use is an APC USB server module. when you're not using the KVM, you can use whatever you want.

by the way you worded it, none of your servers work with AP5253 and AP5201? may i ask what model servers these are - are they all the same? you should have the black end connected to the AP5201 and the blue VGA end/USB connected to the server. i only mention this because i recently came across a similar case with a cable connected backwards so forgive me if that sounds obvious.

let me know what you find out there and then i have a few more ideas that we can take offline if its ok. i will send you an email if the email in your profile is correct.

do you have any other devices connected with any other modules besides AP5253 that are working properly?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

0 Likes
0
2554
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

None of the servers work with the APC USB cable. We have a real mix from 5 year old IBM to HP to 3 month old Dell. Any server connected with the older PS2 cable works just fine.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

0 Likes
0
2554
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

and sorry, i couldnt tell from any of these posts - this is with (1) AP5253 or multiple AP5253 USB modules?

let me know and i have an idea we can try.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

0 Likes
0
2554
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

to find the firmware version of the KVM, you need to bring up the OSD on the KVM and then go to the ADM menu, which I think is if you press F4. then press down arrow until you see firmware upgrade. press enter on that option, and it will display the firmware version. you will see something like 1.3.323. let me know what you see in there and if it can be upgraded, i can help you with that procedure.

what part numbers are you using for the APC cables? these are the only ones that should work and the only ones we would support. also, what types of servers are these?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

0 Likes
0
2554
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:51 PM . Last Modified: ‎2024-03-20 03:43 AM

Was there ever a resolution on this? As I appear to have the same issue. 

Connecting an AP5719 through an AP5201 using the AP5253 and have video but no mouse or keyboard. 

Keyboard on AP5719 works ok into AP5201 for OSD and hotkeys. 

USB mouse and keyboard plugged directly into Dell R330 server work fine. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore