Hi all
I have a Backup-UPS Pro 900G which has been showing a strange behaviour lately. The connected NAS reports that the 900G repeatedly (always at a full or almost full hour) switches to battery mode and within a minute back to AC mode. There are 1-2 of these events per day. Is this normal?
Another question. Is there a software with which I can control the behaviour of the 900G from a remote PC. Both the 900G and the PC are connected to the local LAN.
Thanks a lot for any help.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:34 AM . Last Modified: 2024-03-27 01:37 AM
Hi Bill
thanks for your response.
I have no idea if there is something happening on the power side when the 900G goes to battery mode for a few seconds.If this is not a known behaviour, I will try to figure out if there is a pattern in the times (besides always being around the full hour) that might give some hints.
Rudi
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:34 AM . Last Modified: 2024-03-27 01:37 AM
Hi,
You can only connect 1 device to the Back-UPS USB port. If you would like to connect the PC you must first disconnect the NAS then connect the PC and assuming the PC is running a version of Windows os you can install PowerChute Personal Edition on the PC to monitor / control the Back-UPS.
What is happening at the time that the NAS reports the UPS is on battery? Is there a power failure, sage or increase in the incoming power?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:34 AM . Last Modified: 2024-03-27 01:37 AM
Hi Bill
thanks for your response.
I have no idea if there is something happening on the power side when the 900G goes to battery mode for a few seconds.If this is not a known behaviour, I will try to figure out if there is a pattern in the times (besides always being around the full hour) that might give some hints.
Rudi