80kVA UPS Load Curve

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • 80kVA UPS Load Curve
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

0 Likes
5
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

80kVA UPS Load Curve

I have an 80kVA UPS which will be loaded gradually whilst our upstream supply network is being upgraded.

To start, the UPS will be loaded to 25%. I would like to know what current on the input side the UPS will be drawing from my mains. This load will be gradually increased over time to 50%. I have been told there is a load curve that I can use to estimate my input currents but do not find it anywhere. Can anyone help me please?

The UPS is rated for 150A input whilst supplying the full 80kVA load.

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
cmarler_apc
Lieutenant JG cmarler_apc
Lieutenant JG

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

Congratulations, Matso! You picked a fine unit. I'm sorry if this reply is late. I didn't log on to check the forums until the weekend.

The Redundant intelligent module (RIM) is there for redundancy, and the main intelligence module (MIM) will work without it. The UPS can take load right away, so no worries there.

Your load will not drop, even if the remaining intelligence module goes faulty. Don't worry, your UPS will work fine. The static bypass will switch over if there is a problem with the UPS and it can't carry the load, without any switching transients that will affect the load.

good luck!

-Chuck

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
cmarler_apc
Lieutenant JG cmarler_apc
Lieutenant JG

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

Hi there Matso,

Please respond to this forum thread with some additional information. The specific information I need to form an intelligent response to your question is the part number or model of the UPS you are referring to. Is it a Silcon 80KVA UPS? Is it a Symettra PX UPS? Did you buy this as part of an InfraStruXure solution? What is the ISX solution number on your order? How old is this UPS? What is the incoming voltage of the UPS? What is the output voltage? What is the part number or model number of the PDU (Power Distribution Unit) supplying incoming electrical service to the UPS? ..and most importantly, what is the power factor of the load connected to the output of the UPS. Is it 1:1power factor corrected switched mode power supplies of computing/network equipment manufactured after 2003? I ask all these questions because different models of UPS have different input current draws for different output current draws, based on the efficiency curves of the UPS at different load levels and the power factor of the electrical load. Trust me, I'm not just asking technical questions you can't answer just to avoid giving you an answer. I love giving people answers they can use.

I'll check back later to see your response.

All the best!

-Chuck

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

Hi Chuck,

Here's the info you had requested:

1. The part number or model of the UPS you are referring to.
Model SYCF80KH

2. Is it a Silcon 80KVA UPS? Is it a Symettra PX UPS?
Symmetra PX 10-80kW 3x400/230V

3. Did you buy this as part of an InfraStruXure solution?
I'm only involved in supplying power to the UPS and conecting the load. Another department ordered the unit.

4. What is the ISX solution number on your order?
PDU ISX Number ISX519605-002

5. How old is this UPS?
NEW

6. What is the incoming voltage of the UPS?
400V

7. What is the output voltage?
230V

8. What is the part number or model number of the PDU (Power Distribution Unit) supplying incoming electrical service to the UPS?
PSX-PDU239V#468110
Serial No: DF0804010008

9. What is the power factor of the load connected to the output of the UPS. Is it 1:1power factor corrected switched mode power supplies of computing/network equipment manufactured after 2003?
The load is a number of IT Servers, some old and others new.

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

cmarler_apc
Lieutenant JG cmarler_apc
Lieutenant JG

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

Thanks Matso,
If you have it up and running, the PDU front panel power view display should show you what your phase current draw is on incoming line conditions, based on the incoming voltage.

Assuming a 97% efficiency of the PDU transformer, it has Nominal Current draw of 116A and a Maximum Current draw of 144A.
Assuming you have nominal 400V input, during normal operation for 3 phase current draw on the mains,
at 25% load you can expect to draw approximately on the mains input 35 amps
at 50% load you can expect to draw approximately on the mains input 70 amps

Main service disconnect must be sized at 200A

the manuals are at
UPS Site Prep Manual --> http://www.apcmedia.com/salestools/ASTE-6Z4KNN_R0_EN.pdf
PDU Manual --> http://www.apcmedia.com/salestools/ASTE-6YWKJ5_R0_EN.pdf

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

Hi Chuck,

Thanks for your response last time.

My new question:

The UPS was commissioned in the early hours of this morning. We however have one problem, one of the Intelligent Modules (RIM) is faulty.

My problem is that we need the UPS to take load right away. Can the UPS be able to work with just one intelligent module? If the remaining IM also goes faulty, will the UPS be able to go to Static By-pass and not let the load to be dropped?

As always, your speedy, considered respeonse will be highly appreciated.

Thank you

Matsobane

Reply

Link copied. Please paste this link to share this article on your social media post.

cmarler_apc
Lieutenant JG cmarler_apc
Lieutenant JG

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

0 Likes
0
1630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:39 PM . Last Modified: ‎2024-03-21 03:27 AM

Congratulations, Matso! You picked a fine unit. I'm sorry if this reply is late. I didn't log on to check the forums until the weekend.

The Redundant intelligent module (RIM) is there for redundancy, and the main intelligence module (MIM) will work without it. The UPS can take load right away, so no worries there.

Your load will not drop, even if the remaining intelligence module goes faulty. Don't worry, your UPS will work fine. The static bypass will switch over if there is a problem with the UPS and it can't carry the load, without any switching transients that will affect the load.

good luck!

-Chuck

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of