2 x UPS 3000 failures - both at the same time

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • 2 x UPS 3000 failures - both at the same time
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-27 02:16 AM

0 Likes
4
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-27 02:16 AM

2 x UPS 3000 failures - both at the same time

Hey guys, 

Looking for some advice here - 


I've got 2 x IBM UPS 3000s (IBM 3000XLV 3000VA Rackmount 2U Online UPS) in operation in our server room.
Today when I went into the server room I noticed they were were both making blip sounds and neither have any display or respond to the buttons on the front.
They are both however still supplying power to all connected devices. I imagine if the power went out they'd be useless though.
Both were totally fine yesterday and chugging away as usual with < 50% load each.

Couldn't really find anything that described exactly what I was seeing after searching around for a while so a video will be best to show it:
https://youtu.be/PrGGFSxraLE
The top one is doing the same thing, just not as frequently.

I've tried removing the load on one, unplugging the power and disconnecting the battery and leaving it off for a while.
It just resumes blipping away when I plug it back in and there doesn't seem to be any life with the interface, NIC, etc.
I have also tried another power outlet with the same results but it's on the same circuit and I don't have any others to test with in the office.

Have these both just suddenly fried at exactly the same time, perhaps due to some kind of power event?
Is there anything else I can try to attempt to revive these units?

Cheers,
Mark.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-27 02:15 AM

0 Likes
0
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-27 02:15 AM

Yeah these weren't being monitored at all and there were no plans to (not my call) so no logs of any kind.
Warranty was out in 2009 so I guess they'll have to replaced.

Appreciate the tips and assistance!

Cheers,
Mark.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-27 02:16 AM

0 Likes
0
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-27 02:16 AM

Mark,

Are there network cards in the UPS? If so the event log or data should show what happened. If you don't have network cards but you have PowerChute Business Edition or APCUPSD configured with the units the event log in the software should show what happened. 

The flashing is an indication of an internal fault. You can run a reset of the units (see kbase FA156611). If that does not resolve the issue the units should be replaced.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-27 02:16 AM

0 Likes
0
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-27 02:16 AM

Yes they both have built in NICs, there's no activity on the switch port or the port on the UPS though.
I presume that means that's not going to be of any help.

I tried the instructions as mentioned here:
http://www.schneider-electric.us/sites/us/en/support/faq/faq_main.page?page=content&country=US〈=en&l...

Nothing... neither of the buttons on the front are responsive and they do absolutely nothing whether the power is unplugged or plugged in at the wall.
With or without the battery attached made no difference either. I guess that means they are toast...


What could have caused this to happen? Both at the same time is pretty coincidental so I'm doubting it just happened randomly out of the blue, and was more likely to have been caused by some specific event.

Cheers,
Mark.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-27 02:15 AM

0 Likes
0
973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-27 02:15 AM

Hi,

Without having the logs I am only speculating but a surge or spike may be the culprit. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-27 02:15 AM

0 Likes
0
974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-27 02:15 AM

Yeah these weren't being monitored at all and there were no plans to (not my call) so no logs of any kind.
Warranty was out in 2009 so I guess they'll have to replaced.

Appreciate the tips and assistance!

Cheers,
Mark.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore