2 Model BR1500MS Caught Fire

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • 2 Model BR1500MS Caught Fire
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:10 AM . Last Modified: ‎2024-03-26 03:37 AM

0 Likes
16
6663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:10 AM . Last Modified: ‎2024-03-26 03:37 AM

2 Model BR1500MS Caught Fire

Back in April, we had 2 new BR1500MS units that caught fire at a customer site within 4 months of each other.  The fire was put out before it caused damage to the building but the customer has major concerns and is removing all the APC units.  We reached out to APC and they told us the following:

"As of the moment, you can tell your clients about the possible cause, the MOV (internal component) of the APC unit might be burned out that causes the problem, it might be on the high voltage that came from the outlet or the component is being defective itself. Further examination will be done for your unit in a couple of weeks."

It has been months now and we still haven't heard back on the final outcome of the cause of the fire.  Has anyone run into similar issues with this model during this time frame?  It seems strange that our customer would be the only one that this happened to if there was a defect with the model.  

We also wanted to make others customers aware that we had this happen so they could take any necessary precautions as well.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • br1500ms
  • burnt
  • fire
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

0 Likes
0
6661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

The replacement BR1500MS2 was delivered and I connected it today.  I hope it lasts longer than the last 2 model BR1500MS units did.  Only time will tell.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 16
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:10 AM . Last Modified: ‎2024-03-26 03:37 AM

0 Likes
0
6661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:10 AM . Last Modified: ‎2024-03-26 03:37 AM

Hi,

You should contact local support. They should replace the unit and take it back for investigation. 

Local support contact information will be found at this link.

https://www.apc.com/us/en/support/contact-us/index.jsp

You may need to change the region in the upper left of the contact us web page. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:10 AM . Last Modified: ‎2024-03-26 03:37 AM

0 Likes
0
6661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:10 AM . Last Modified: ‎2024-03-26 03:37 AM

I received a prompt replacement from APC when my first BR1500ms popped, smoked, and died.   Unfortunately, about 2 weeks after receiving the replacement, the same thing happened.    Nothing was happening when it popped.   No suggestion of a power surge.   I've used that outlet with regular surge suppressors for years with no trouble.   Is this a problem with this model ?   I don't want to just get the same model again....

 

Duncan

  • Tags:
  • back-ups
  • br1500ms
  • problem
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:10 AM . Last Modified: ‎2024-03-26 03:37 AM

0 Likes
0
6661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:10 AM . Last Modified: ‎2024-03-26 03:37 AM

Hi Duncan,

Can you send me you case number from support and I can have a look?

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:37 AM

0 Likes
0
6661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:37 AM

I am having the same problem. My first unit dies within a week, I got a replacement unit and it died today, less than two weeks from the first failure. I was sitting here this time and it popped and black acrid smoke came pouring out. The smell in my house from these two events is nauseating. But more important, there seems ot be a design defect here. Read the reviews on some of the retail web sites and it seems that this failure may be very common. I now have a third unit being delivered. the test date on my first unit was late July 2020, the last unit was June 21, 2020. I don't know if there has been a design change to this model but if there is, I would really like the latest version. My fear is I am going to be in an endless cycle of APC sending me replacements only to have them fail within a few weeks and doing it all over again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

0 Likes
0
6661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

I bought a BR1500MS in June 2020 and all was fine until this past Friday morning.  I noticed the familiar smell of burning electronics and then a pop sound.  It dropped power to all connected devices, displayed the F02 error code and began smoking.  Luckily, I was sitting right here and was able to quickly unplug everything before it may have caught fire. It has a very light load on it. 1 desktop, 1 laptop, 2 monitors (battery backup outlets) and 1 printer (surge protected outlet).

I bought the unit from Amazon and found several product reviews voicing the same complaint.

I contacted Support and since it was still under warranty, they authorized a replacement unit to be shipped.  I hope to have the replacement by the end of the week, but now I'm beginning to question my decision about buying this unit.  I should have paid more attention to the bad customer reviews.

The one question I failed to ask is if the replacement unit will have a new 3-year warranty or if it picks up from the original June 2020 purchase date.

  • Tags:
  • br1500ms
  • f02
  • fire
  • smoke
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

0 Likes
0
6660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

I just had the same problem on one of the two I have.  The process for the F02 error is to turn the unit off and disconnect everything then turn it back on to test which device was causing the problem.  

When I turned mine on, I got sparking and a strong burning smell.

Two days after that incident with the battery removed, I tried again.  Now all it does is go to the F02 error after 10 seconds.  I can remove the battery and turn it on and the display will stay on.  It appears the Battery part of the unit has failed..

It is only 8 months old but has been in service only about 5 months.  I am currently waiting to hear back regarding the service claim..  Since this was reported on Jan 20, 2021, maybe it will take more time..

Thanks ..

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

0 Likes
0
6660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

When mine burned up last Nov. 6, I contacted support via the online chat.  After answering a few basic questions, they authorized sending me a replacement unit which I received on Nov. 12.  I used that packaging to return the defective unit.

The replacement unit is still working, so far, but it's only been a little more than 2 months so I am not willing claim victory quite yet.

Good luck!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

0 Likes
0
6660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

Thanks Gary, I just completed that process and the RMA is in the works.  It did appear the chat agent did not have access to the Case number already set up.

My other unit has been in service longer and is my backup for my gaming computer.  The bad system had a very light load.  Maybe light loads are involved with some failures.  Perhaps letting the system run on Battery, in addition to is normal checks, for some time every now and then, might help keep it functional.

Thanks Again,

Clark

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

0 Likes
0
6661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

Mine also has a very light load - 80 watts or less.  Two PCs, two monitors plugged into battery backup outlets and 1 LJ printer plugged into a surge protected only outlet.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

0 Likes
0
6660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

Since I replaced my second unit in only a few weeks due to the fire and F02 fault in mid October this third unit has been running flawlessly. It has been threw a couple of power outages and several line events as registered by the unit but is still hanging in there (knock on wood). I also run a very light load; PC, monitor, Router, Wireless AP.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

0 Likes
0
6661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

My 1.5yr old APC BR1500MS also blew up with sparks and smoke yesterday with F01 fault (overload on output) and then F02 (solid state component damage) . They are apparently replacing it under warranty with a new version BR1500MS2 and want the burnt one back.  They obviously know there is a problem and should have done a recall. It could have burnt my house down if no one was home.  Anyone having an incident like this with an APC UPS should report it to CPSC US or CPSD Canada.  

I am an Electrical Engineer and have never been scared of any electronics in my home before because the the 120VAC supply is fused, but a UPS has a really big battery to supply power to a shorted output stage. Field Effect Transistors (FETs) are notorious for failing shorted.

Really scary situation....

  • Tags:
  • br1500ms
  • f01
  • f02
  • fire
  • smoke
  • sparks
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

0 Likes
0
6661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

Well, the warranty replacement unit APC sent me Nov 2020, died last evening the same way the original one did - loud "pop" a puff of smoke and the unmistakable smell of burning electronics.  Again, glad I was sitting here so I could immediately disconnect it.

I emailed customer support and told them I wanted my money back and not another replacement unit.  Time to look for another brand.  I'll have to wait and see how they reply.

I've had various APC units over the years and never had problems like this. Very disappointing.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

0 Likes
0
6661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

I was finally able to get in touch with APC support via online chat.  I requested a refund since the second BR1500MS burned up and died.  Since I purchased it from Amazon, they will not refund my money but will honor the original 3-year warranty.  They are replacing it with the "upgraded" BR1500MS2.

I went back to Amazon to update my review and discovered that the product page could no longer be found. surprised

I suspect that they had significant failures of the BR1500MS but rather than issuing a recall or notifying customers of the problem, they redesigned the unit and called it BR1500MS2.  Time will tell.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

0 Likes
0
6662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:11 AM . Last Modified: ‎2024-03-26 03:36 AM

The replacement BR1500MS2 was delivered and I connected it today.  I hope it lasts longer than the last 2 model BR1500MS units did.  Only time will tell.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-09-20 12:22 PM

0 Likes
1
6525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-20 12:22 PM

This just happened to me over this past weekend. No devices were turned on when it happened. I didnt see any smoke, I did hear the loud pop and beeping noise as well as smell.

 

I'm hoping my desktop that was connected isnt damaged. So far all the major components on it appear to be working. They are sending me a BR1500MS2 as a replacement.

 

Did anyone who had this issue have any damage on their electronics that were connected?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-09-24 11:33 AM

In response to Anonymous user
0 Likes
0
6459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-24 11:33 AM

@Anonymous user 

 

Please contact local Schneider Electric technical support for assistance.

 

Local support contact information will be found at this link.

https://www.apc.com/us/en/support/contact-us/index.jsp

You may need to change the region in the upper left of the contact us web page. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of