I am getting the below messages....
Can any one tell me what this means?? (this is on a Symmetra 40K 3-phase unit)...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-12 12:44 AM . Last Modified: 2024-01-31 03:00 AM
Hi,
I checked with 3 phase support and below is the responses.
Means the Q1 main input to the ups either was opened and closed shortly after or the reporting is a problem with the aux contact circuit showing its status.
You should contact 3 phase support at 800-555-2725 option 4 and they will be happy to assist you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-12 12:44 AM . Last Modified: 2024-01-31 03:00 AM
Hi,
I checked with 3 phase support and below is the responses.
Means the Q1 main input to the ups either was opened and closed shortly after or the reporting is a problem with the aux contact circuit showing its status.
You should contact 3 phase support at 800-555-2725 option 4 and they will be happy to assist you.