Posted: 2021-07-12 12:44 AM
This question was originally posted by Cathy on APC forums on 9/6/2018
I am getting the below messages....
Can any one tell me what this means?? (this is on a Symmetra 40K 3-phase unit)...
thx
Posted: 2021-07-12 12:44 AM
This reply was originally posted by Bill on APC forums on 9/7/2018
Hi,
I checked with 3 phase support and below is the responses.
Means the Q1 main input to the ups either was opened and closed shortly after or the reporting is a problem with the aux contact circuit showing its status.
You should contact 3 phase support at 800-555-2725 option 4 and they will be happy to assist you.
Posted: 2021-07-12 12:44 AM
This reply was originally posted by Bill on APC forums on 9/7/2018
Hi,
I checked with 3 phase support and below is the responses.
Means the Q1 main input to the ups either was opened and closed shortly after or the reporting is a problem with the aux contact circuit showing its status.
You should contact 3 phase support at 800-555-2725 option 4 and they will be happy to assist you.