Failed to perform total power off to Symmetra PX 96/160kw

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Failed to perform total power off to Symmetra PX 96/160kw
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 12:44 AM . Last Modified: ‎2024-02-14 10:12 PM

0 Likes
3
2734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:44 AM . Last Modified: ‎2024-02-14 10:12 PM

Failed to perform total power off to Symmetra PX 96/160kw

I have Symmetra PX 96/160kw that have faulty, the client team change operation mode to maintenance bypass, i.e. total load on utility power.

I receive the alarm  Local Management to UPS lost, the LCD display failed to communicate with the UPS but still can read the lines voltages. 

I have changed the network cards, the intelligent module, the power supply, the communication cables... still no change

I tried to perform a total power off by :

    • Set the UPS SYSTEM ENABLE switch to the OFF position              
    • Set the Q2 switch to the OFF position. 
    • Set the Q1 switch to the OFF position. 
    • Set the Q5 breaker to the OFF position.              
    • Set maintenance bypass switch (Q3) to OFF position.   
    • Set Subfeed breaker to OFF position.   
    • Set the DC DISCONNECT switch to the OFF position on   the PDU with modular batteries              
    • Disconnect all battery units by pulling them out to the red disconnect line          
    • Pull all the power modules out of the cabinet. 
    • Pull out the static bypass module.

unfortunately, the failure to do that and the network card and the LCD display continues to have power and working.

anybody can clarify this issue for me? with thanks.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-12 12:44 AM . Last Modified: ‎2024-02-14 03:18 AM

0 Likes
0
2734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:44 AM . Last Modified: ‎2024-02-14 03:18 AM

I suggest contacting three-phase support for more details:

http://www.apc.com/us/en/support/contact-us/

From what I remember, the modular distribution panel has its own power supply (powered by the UPS output) that runs the metering boards (these measure currents through the modular breakers and subfeeds) as well as running the network card and display. With the UPS off you can still manage the distribution panel.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-12 12:44 AM . Last Modified: ‎2024-02-14 03:18 AM

0 Likes
0
2734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:44 AM . Last Modified: ‎2024-02-14 03:18 AM

The card and display are powered by the modular distribution panel at the output of the UPS. That's also what measures the line voltages. Since the UPS is in bypass, the card and display are still powered.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-12 12:44 AM . Last Modified: ‎2024-01-31 03:00 AM

0 Likes
0
2734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:44 AM . Last Modified: ‎2024-01-31 03:00 AM

Thank you voidstar for information, do you have an SLD showing how LCD display and network card is connected.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-12 12:44 AM . Last Modified: ‎2024-02-14 03:18 AM

0 Likes
0
2735
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-12 12:44 AM . Last Modified: ‎2024-02-14 03:18 AM

I suggest contacting three-phase support for more details:

http://www.apc.com/us/en/support/contact-us/

From what I remember, the modular distribution panel has its own power supply (powered by the UPS output) that runs the metering boards (these measure currents through the modular breakers and subfeeds) as well as running the network card and display. With the UPS off you can still manage the distribution panel.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore