what are metered banks, phases, outlets, switched outlets and how are they monitored?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • what are metered banks, phases, outlets, switched outlets and how are they monitored?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:10 PM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
4
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:10 PM . Last Modified: ‎2024-03-12 01:15 AM

what are metered banks, phases, outlets, switched outlets and how are they monitored?

Hello Guys,

this is my first time working on a metered PDU and i was wondering how can i monitor, metered banks, metered outlets, switched outlets and metered phases and what

do they really mean in Electrical world cause i am purely an IT person.

Regards

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
0
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:15 AM

Hello Angela,

thanks for your kind response this helps a lot for sure, i have well understood most of the terms which made me suffer earlier and now i will use the links you provided me to seek more information. in case i will have anything to share or ask i will get back to you as earlier as possible.

Kind Regards.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
0
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:15 AM

Hello Guys,

this is my first time working on a metered PDU and i was wondering how can i monitor, metered banks, metered outlets, switched outlets and metered phases and what

do they really mean in Electrical world cause i am purely an IT person.

Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
0
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:15 AM

Hello,

A metered PDU (Power Distribution Unit) means the current draw of the PDU is monitored and displayed to the user to understand the power consumption and amperage of the attached equipment (servers, IT equipment, etc). Banks are just "groups" of outlets which some PDUs have and they typically have their own circuit breaker. Most PDUs just metered at the total PDU or the bank level. Some new PDUs allow you to meter or monitor amperage at the outlet level, hence metered outlets. Switched outlets are outlets that have a relay that you can "switch" on and off to turn the equipment plugged into it off remotely. You do this all remotely via a network management interface typically.

Phase refer to phases of power which is best handled here-> Single-phase electric power - Wikipedia, the free encyclopedia - there is single and three phase power. A metered PDU can sometimes report how much current per phase is being drawn depending on the input power to the device.

Hope that helps get you started. Metered and Switched PDUs are intelligent power strips that allow you to see information about the power draw and power consumption for the entire strip, groups of outlets AKA banks, or sometimes for the individual outlets. Switched PDUs specifically allow you to control individual outlets with on, off, or reboot commands. These can also be scripted via multiple methods to help assist with automation. Switched PDUs are also very useful for a user to log in remotely and reboot a "hung" server or similar.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
0
1713
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:15 AM

Hello again,

Thanks for the screenshot. Your PDU model is a metered model, AP8858. You can see it here -> Buy Rack PDU 2G, Metered, ZeroU, 20A/208V, 16A/230V, (18) C13 & (2) C19 - Technical Specifications a...

It does NOT support switched outlets or metering at the outlet level as we have other models that support those features that ultimately cost more.

Because of its size and rating, I also don't think it has multiple banks. That's why in your screenshot it shows 1 phase of power and 0 for the rest since ultimately you have one giant bank which contains all of the outlets on the PDU and is powered by a single phase of power.

You can set thresholds on the metered phase including a low load, warning load, and overload. You do this under Configuration, RPDU, phase menu I think (going off the top of my head). The page I linked you to has the user's guide as well under Documentation tab/section and you want the 6.X.X firmware user documentation based on what I can tell on your firmware version since the interface is green and white. This can help explain some of the functionality for you as well. 


Once you set these thresholds, you can set up email notifications (among other types like SNMP) when they are triggered to alert people. FYI, the default thresholds come preset for what we recommend but you may need to change them based on your application and how much load is typically connected. It also may depend on what region you are in and what the input voltage is to the PDU. This model is used or can be used  in different parts of the world.


Also, separate issue, please check this alert which may apply to you if you're running this firmware version - and we want to update it to prevent a problem -> INFORMATION BULLETIN: Potential Issue with AP8XXX series Rack Power Distribution Units with rpdu2g v...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:15 AM

0 Likes
0
1714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:11 PM . Last Modified: ‎2024-03-12 01:15 AM

Hello Angela,

thanks for your kind response this helps a lot for sure, i have well understood most of the terms which made me suffer earlier and now i will use the links you provided me to seek more information. in case i will have anything to share or ask i will get back to you as earlier as possible.

Kind Regards.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore