surta1500rmxl2u wont come on, has utility power, and battery connected

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • surta1500rmxl2u wont come on, has utility power, and battery connected
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:20 AM . Last Modified: ‎2024-03-12 03:07 AM

0 Likes
3
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:20 AM . Last Modified: ‎2024-03-12 03:07 AM

surta1500rmxl2u wont come on, has utility power, and battery connected

Hello,

I have had 2 of these do the same thing, is there anything I can do to try and troubleshoot without calling APC tech support? Customer has ordered quite a bunch of these, and the last few have done this. Any help will do. Thanks in advance.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:20 AM . Last Modified: ‎2024-03-12 03:07 AM

0 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:20 AM . Last Modified: ‎2024-03-12 03:07 AM

Hi Erin,

These are on a 48V system so the float voltage is 55vDC about. I would expect at least something in the 40's for voltage, especially if everything is very new. I also don't know if the customer has a network management card available either to see if even though the UPS won't turn on, if the Network Management Card powers up in the UPS while it's connected to AC power. PowerChute might be worth a try, just to see if the UPS intelligence is active and can shed any light on why the UPS isn't turning on.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:20 AM . Last Modified: ‎2024-03-12 03:07 AM

0 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:20 AM . Last Modified: ‎2024-03-12 03:07 AM

First thing I would do is want to know how old they (the UPS units) are and if they have been sitting in storage with or without the battery connected. We should also measure the DC voltage on the batteries. These units need good batteries to turn on and the batteries are left connected to the UPS but the UPS is not plugged in, then the batteries will discharge in the UPS and be too low of a voltage to be able to turn the UPS on.

The other thing you'd want to try, perhaps even first, is cold start the UPS. Remove it from AC power/unplug it and hold down the test/on button and see if you hear any beeps. If you do, it should be two, and let go during the second. This would attempt to start the UPS off of battery power and at least tell you that the UPS is operation without some potential variable from the input power source causing an issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:20 AM . Last Modified: ‎2024-03-12 03:07 AM

0 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:20 AM . Last Modified: ‎2024-03-12 03:07 AM

These units were just purchased within the last month from APC. The one in question was just ordered 2 weeks ago, just took it out of the box and tried to install it. I did try the coldstart, it did nothing. Could it be the batteries? What should the voltage be from the battery pack so I can let the customer know and possibly get him to measure. Thank you Angela for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:20 AM . Last Modified: ‎2024-03-12 03:07 AM

0 Likes
0
1444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:20 AM . Last Modified: ‎2024-03-12 03:07 AM

Hi Erin,

These are on a 48V system so the float voltage is 55vDC about. I would expect at least something in the 40's for voltage, especially if everything is very new. I also don't know if the customer has a network management card available either to see if even though the UPS won't turn on, if the Network Management Card powers up in the UPS while it's connected to AC power. PowerChute might be worth a try, just to see if the UPS intelligence is active and can shed any light on why the UPS isn't turning on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore