sua3000xl issue with 1 row of outlets

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • sua3000xl issue with 1 row of outlets
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

0 Likes
2
726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

sua3000xl issue with 1 row of outlets

We have a new sua3000xl that has the bottom row of outlets not operational.  We tried resetting with the white button to the right of the row, and that didn't solve the issue.  We will likely seek and RMA, but I wanted to see if there is anything else to try.

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • outlets
  • sua3000xl
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

0 Likes
0
725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

Thank you for your prompt reply.  We followed your steps and opened the backplate.  We found an unseated Molex connector going to the 3rd row reset breaker.  Fixing that resolved the issue.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

0 Likes
0
725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

I believe the Power Distribution (PDU) backplates can be swapped on this unit. If I were you, I'd fully power down the unit and remove its battery and essentially "braindead" the unit. Braindeading is when you unplug the UPS from AC power and then hold down the (o) off button and wait till you hear the UPS click and/or flash its front panel's LEDs. I'd then just remove the battery to be safe.

Once you do that, you can remove the screws on the PDU backplate where the outlets are and they should have arrows pointing to the ones you remove. When you take the backplate off, check all the molex connectors to see if one is loose or disconnected which could cause the row of outlets not to work. This is worth a check before you go through an RMA process.

FYI, we have a video knowledge base on how to do this -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA156589 

And just in case anyone else sees this, these backplates are only designed to be removed/replaced by the user and thus there are safety precautions in place to prevent shocks or hazards. This cannot be done on all Smart-UPS or UPSs in general so before proceeding, double check for your model. The specific model SKU SUA3000XL has removable backplates and is safe to proceed on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

0 Likes
0
726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:44 AM . Last Modified: ‎2024-02-14 10:49 PM

Thank you for your prompt reply.  We followed your steps and opened the backplate.  We found an unseated Molex connector going to the 3rd row reset breaker.  Fixing that resolved the issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of