snmp OIDs for output current/power

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • snmp OIDs for output current/power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Kola
Crewman Kola
Crewman

Posted: ‎2023-03-22 10:36 AM

0 Likes
4
3499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-22 10:36 AM

snmp OIDs for output current/power

I have an SRT 8KXLI UPS and a Easy Metered PDU (EPDU1016M).
Does anyone know the OIDs for getting info about output current or power from these?

 

This seems almost right for the UPS: .1.3.6.1.4.1.318.1.1.1.4.2.4.0

But i just get a '4', and i was hoping for a bit more resolution than just an integer:)

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Shaun
Commander Shaun Commander
Commander

Posted: ‎2023-03-22 01:36 PM . Last Modified: ‎2023-03-22 01:39 PM

0 Likes
0
3482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-22 01:36 PM . Last Modified: ‎2023-03-22 01:39 PM

Hi,

 

You can find the current version of the mib @ https://www.se.com/ww/en/download/document/APC_POWERNETMIB_446_EN/

 

I show that OID as ePDUPhaseStatusCurrent.1 - "Indicates the Phase Current. Units:0.01 A".  So for a single-phase PDU, that'll give you the PDU overall.  So I learnt something here too.  My -smbo model reports rPDU2 oids, it appears the -m model reports ePDU oids.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Shaun
Commander Shaun Commander
Commander

Posted: ‎2023-03-22 10:49 AM

0 Likes
1
3493
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-22 10:49 AM

For the UPS, see if yours has .1.3.6.1.4.1.318.1.1.1.4.3.4.0 (upsHighPrecOutputCurrent) available. This should be the same measurement to 10ths of an amp (eg, an integer 40 would represent 4.0 amps).

 

For the PDU I'd expect the same from .1.3.6.1.4.1.318.1.1.26.9.4.3.1.6.n (rPDU2OutletMeteredStatusCurrent.n, where n is the outlet number, numbered 1 upwards), but I don't have the same model handy to compare.

Reply

Link copied. Please paste this link to share this article on your social media post.

Kola
Crewman Kola
Crewman

Posted: ‎2023-03-22 12:53 PM . Last Modified: ‎2023-03-22 12:54 PM

In response to Shaun
0 Likes
0
3485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-22 12:53 PM . Last Modified: ‎2023-03-22 12:54 PM

Hey @Shaun Thanks!

The one for the UPS was spot on!

The one for the PDU wasnt there, but i now found 
iso.3.6.1.4.1.318.1.1.30.4.2.1.5.1 = INTEGER: 420   (hundreds i guess)
Looks about right, but i have no clue where to find the MIB to verify:) Cant find it on the APC website.
Will unplug a few things from the PDU tomorrow to verify if the int follows along.

Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Commander Shaun Commander
Commander

Posted: ‎2023-03-22 01:36 PM . Last Modified: ‎2023-03-22 01:39 PM

0 Likes
0
3483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-22 01:36 PM . Last Modified: ‎2023-03-22 01:39 PM

Hi,

 

You can find the current version of the mib @ https://www.se.com/ww/en/download/document/APC_POWERNETMIB_446_EN/

 

I show that OID as ePDUPhaseStatusCurrent.1 - "Indicates the Phase Current. Units:0.01 A".  So for a single-phase PDU, that'll give you the PDU overall.  So I learnt something here too.  My -smbo model reports rPDU2 oids, it appears the -m model reports ePDU oids.

Reply

Link copied. Please paste this link to share this article on your social media post.

Kola
Crewman Kola
Crewman

Posted: ‎2023-03-23 06:05 AM

0 Likes
0
3473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-23 06:05 AM

Thanks a lot @Shaun !

One of these days i must learn how MIBs and such really work, and how to use them:)

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore