Posted: 2023-03-22 10:36 AM
I have an SRT 8KXLI UPS and a Easy Metered PDU (EPDU1016M).
Does anyone know the OIDs for getting info about output current or power from these?
This seems almost right for the UPS: .1.3.6.1.4.1.318.1.1.1.4.2.4.0
But i just get a '4', and i was hoping for a bit more resolution than just an integer:)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-22 01:36 PM . Last Modified: 2023-03-22 01:39 PM
Hi,
You can find the current version of the mib @ https://www.se.com/ww/en/download/document/APC_POWERNETMIB_446_EN/
I show that OID as ePDUPhaseStatusCurrent.1 - "Indicates the Phase Current. Units:0.01 A". So for a single-phase PDU, that'll give you the PDU overall. So I learnt something here too. My -smbo model reports rPDU2 oids, it appears the -m model reports ePDU oids.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-22 10:49 AM
For the UPS, see if yours has .1.3.6.1.4.1.318.1.1.1.4.3.4.0 (upsHighPrecOutputCurrent) available. This should be the same measurement to 10ths of an amp (eg, an integer 40 would represent 4.0 amps).
For the PDU I'd expect the same from .1.3.6.1.4.1.318.1.1.26.9.4.3.1.6.n (rPDU2OutletMeteredStatusCurrent.n, where n is the outlet number, numbered 1 upwards), but I don't have the same model handy to compare.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-22 12:53 PM . Last Modified: 2023-03-22 12:54 PM
Hey @Shaun Thanks!
The one for the UPS was spot on!
The one for the PDU wasnt there, but i now found
iso.3.6.1.4.1.318.1.1.30.4.2.1.5.1 = INTEGER: 420 (hundreds i guess)
Looks about right, but i have no clue where to find the MIB to verify:) Cant find it on the APC website.
Will unplug a few things from the PDU tomorrow to verify if the int follows along.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-22 01:36 PM . Last Modified: 2023-03-22 01:39 PM
Hi,
You can find the current version of the mib @ https://www.se.com/ww/en/download/document/APC_POWERNETMIB_446_EN/
I show that OID as ePDUPhaseStatusCurrent.1 - "Indicates the Phase Current. Units:0.01 A". So for a single-phase PDU, that'll give you the PDU overall. So I learnt something here too. My -smbo model reports rPDU2 oids, it appears the -m model reports ePDU oids.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-23 06:05 AM
Thanks a lot @Shaun !
One of these days i must learn how MIBs and such really work, and how to use them:)