silcon 60KVA high current on battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • silcon 60KVA high current on battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:30 AM . Last Modified: ‎2024-03-19 01:26 AM

0 Likes
7
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:30 AM . Last Modified: ‎2024-03-19 01:26 AM

silcon 60KVA high current on battery

Hi Guys

If the battery current of the Silcon 60KVA will reach up to 155 Amps, what are the possibility/ extent of damage to the UPS? Or is this possible to reach 155 Amps for battery current? Please advice thanks

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:31 AM . Last Modified: ‎2024-03-19 01:26 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:31 AM . Last Modified: ‎2024-03-19 01:26 AM

Hi Guys

If the battery current of the Silcon 60KVA will reach up to 155 Amps, what are the possibility/ extent of damage to the UPS? Or is this possible to reach 155 Amps for battery current? Please advice thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:30 AM . Last Modified: ‎2024-03-19 01:26 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:30 AM . Last Modified: ‎2024-03-19 01:26 AM

if the battery decrease the current increase? are you referring V=IR formula?
Anyway we can say that the board inside of the UPS are safe? the Units is 400V input. Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:30 AM . Last Modified: ‎2024-03-19 01:26 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:30 AM . Last Modified: ‎2024-03-19 01:26 AM

Any 3 phase guy from APC can give me an idea? thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 04:31 AM . Last Modified: ‎2024-03-19 01:26 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:31 AM . Last Modified: ‎2024-03-19 01:26 AM

Actually I'm refering to P=IE

P power being drawn from the battery to supply the load

I current from the battery

E battery string voltage

As the batteries discharge the voltage starts to drop. So as E drops I has to increase to keep P constant.

Once the DC bus reaches a certain low voltage the UPS shuts off the output to prevent the battery level from dropping to low. The prevents current from reaching extemely high levels trying to keep P constant.

Hope this makes sense. If you are blowing or tripping DC fuses/breakers you may have others issues and I would recommend calling into 3 phase tech support.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:31 AM . Last Modified: ‎2024-03-19 01:26 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:31 AM . Last Modified: ‎2024-03-19 01:26 AM

thanks i got it,

the fuse/breaker are all ok.., yeah i email the tech support near our country but i haven't get any feedback from there side.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:31 AM . Last Modified: ‎2024-03-19 01:26 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:31 AM . Last Modified: ‎2024-03-19 01:26 AM

Hi,

Are you refering to the displayed battery current?

If yes your UPS should be locked in static bypass , with a red LED...

There is a DC sense board in Silcon that is responsible for this measurement...

Usually it will need replacement...

Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:31 AM . Last Modified: ‎2024-03-19 01:26 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:31 AM . Last Modified: ‎2024-03-19 01:26 AM

Hi Hazem

yeah on the display and also in the log event, but the battery current on the display and from the log event is different

the log event was quite lower than from the display.

so if the dc sense board is faulty, do you any idea whats the cause why the board got spoiled?

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:31 AM . Last Modified: ‎2024-03-19 01:26 AM

0 Likes
0
867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:31 AM . Last Modified: ‎2024-03-19 01:26 AM

Hi Guys

If the battery current of the Silcon 60KVA will reach up to 155 Amps, what are the possibility/ extent of damage to the UPS? Or is this possible to reach 155 Amps for battery current? Please advice thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore