shutdown procedure - when is the power off for the outlet triggered ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • shutdown procedure - when is the power off for the outlet triggered ?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
bernd_apc
Ensign bernd_apc
Ensign

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-17 11:11 PM

0 Likes
5
2994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-17 11:11 PM

shutdown procedure - when is the power off for the outlet triggered ?

Hi,

we have a new SRT 3000 XLI with NMC AP9630 and Firmware UPS 05.3.
Currently i'm testing. We have several server with PCNS 4.2
If i understand everything right, the time when the server shutdown is configured in PCNS, not in the UPS.
My idea is to keep the server going for 10 minutes, then shutdown them. For the shutdown i'd like to have enough time, if a service does not stop immediately or the umount of a fs takes some time (server are Linux systems).
Let's say 15 minutes. After these 15 minutes i want that the ups switches off the outlet groups.
But when is the switch off of the outlet group triggered ? When the "Low battery duration" is reached ?
What is if i have a power off delay for an outlet group configured ?
Is that the same as the "Low Battery duration", or does the low battery duration triggers the power off delay for the outlet group and then it needs again the time configured for the power off delay ?
And what is the "Basic  low battery duration" ? Is that relevant if i have PCNS ?

Thanks.

Bernd

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
bernd_apc
Ensign bernd_apc
Ensign

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-15 06:16 AM

0 Likes
0
2993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-15 06:16 AM

Hi Bill,

thanks for your message. It's working now. I choosed to start from the end. I configured "Low Battery Duration" with 20 minutes, now UPS will shutdown the servers when only 20 minutes of runtime are left. That does work properly, and also the outlets are turned off 20 minutes after beginn of shutdown.
I'm testing now if my server (HP Proliant ML 350) will boot automatically when the outlets are turned on again.

Bernd

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-17 11:11 PM

0 Likes
0
2993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-17 11:11 PM

HI,

On 1/25/2019 10:45 AM, Bernd said:

If i understand everything right, the time when the server shutdown is configured in PCNS, not in the UPS.

It can be done in either PCNS or the NMC since they UPS has switched outlet groups. 

On 1/25/2019 10:45 AM, Bernd said:

My idea is to keep the server going for 10 minutes, then shutdown them. For the shutdown i'd like to have enough time, if a service does not stop immediately or the umount of a fs takes some time (server are Linux systems).

You can do this in PCNS by selecting Configure Events - UPS on Battery - Shutdown and set the delay to 600 seconds. After the UPS has run on battery for 10 minutes PCNS will command the OS down. 

On 1/25/2019 10:45 AM, Bernd said:

Let's say 15 minutes. After these 15 minutes i want that the ups switches off the outlet groups.

To have the outlet groups power off 15 minutes after the OS is commended down in PCNS under Shutdown Settings select Turn off UPS. Then in the NMC web interface set the outlet off delay to 900 seconds. When PCNS tell the OS to power down it will send a signal to the NMC to tell the UPS / outlet groups to power down. The outlet groups will wait the delay set and then cut power. 

NOTE: The main outlet group will not begin the power down cycle until all of the switched outlet groups are off / power down. So if you set a power off delay of 900 seconds for the switched outlet groups and 900 seconds for the main the switched will count down the delay and power off. Then the main will count down the 900 second delay and power off so from the time that the power off command is received the main will wait 1800 seconds before powering down.

There is a way to get the main to power down at the same time as the switched. I would need to know what outlet group/s the PCNS clients are plugged into and how you would like the main to react before offering a recommendation. 

On 1/25/2019 10:45 AM, Bernd said:

But when is the switch off of the outlet group triggered ? When the "Low battery duration" is reached ?
What is if i have a power off delay for an outlet group configured ?
Is that the same as the "Low Battery duration", or does the low battery duration triggers the power off delay for the outlet group and then it needs again the time configured for the power off delay ?
And what is the "Basic  low battery duration" ? Is that relevant if i have PCNS ?

Low battery duration and basic low battery duration are both explained in the NMC help file. 

Low battery duration will trigger PCNS to command the OS down and trigger the outlet off delay count down. Basic low battery duration is not used by PCNS. 

Reply

Link copied. Please paste this link to share this article on your social media post.

bernd_apc
Ensign bernd_apc
Ensign

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-17 11:11 PM

0 Likes
0
2993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-17 11:11 PM

On 25/01/2019 18:51, Bill said:

To have the outlet groups power off 15 minutes after the OS is commended down in PCNS under Shutdown Settings select Turn off UPS. Then in the NMC web interface set the outlet off delay to 900 seconds. When PCNS tell the OS to power down it will send a signal to the NMC to tell the UPS / outlet groups to power down. The outlet groups will wait the delay set and then cut power. 

I will try that.

On 25/01/2019 18:51, Bill said:

NOTE: The main outlet group will not begin the power down cycle until all of the switched outlet groups are off / power down. So if you set a power off delay of 900 seconds for the switched outlet groups and 900 seconds for the main the switched will count down the delay and power off. Then the main will count down the 900 second delay and power off so from the time that the power off command is received the main will wait 1800 seconds before powering down.

There is a way to get the main to power down at the same time as the switched. I would need to know what outlet group/s the PCNS clients are plugged into and how you would like the main to react before offering a recommendation. 

I don't have a main outlet.

On 25/01/2019 18:51, Bill said:

Low battery duration will trigger PCNS to command the OS down and trigger the outlet off delay count down.

I think that's not right. I tested it but the outlets weren't switched off after the delay.

Bernd

Reply

Link copied. Please paste this link to share this article on your social media post.

bernd_apc
Ensign bernd_apc
Ensign

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-17 11:11 PM

0 Likes
0
2993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-17 11:11 PM

On 25/01/2019 18:51, Bill said:

To have the outlet groups power off 15 minutes after the OS is commended down in PCNS under Shutdown Settings select Turn off UPS. Then in the NMC web interface set the outlet off delay to 900 seconds. When PCNS tell the OS to power down it will send a signal to the NMC to tell the UPS / outlet groups to power down. The outlet groups will wait the delay set and then cut power. 

It does not work. I configured the PCNS to shutdown the server after 5 minutes on battery. Following the log of the PCNS:

30.01.2019 18:20:49 Shutting down physical machine that PowerChute is running on.
30.01.2019 18:20:49 PowerChute is turning off UPS 10.35.23.113
30.01.2019 18:20:49 Shutdown process started. Linux will shut down soon.
30.01.2019 18:20:49 UPS critical event: On Battery.
30.01.2019 18:15:49 UPS has switched to battery power.

I choosed once "Turn off the UPS" and once "Turn off the UPS Outlet Group" in the settings of PCNS.
In both cases servers were shutdown after 5 minutes, and PCNS sent a signal to the UPS, but neither UPS nor Outlet Group switched off. What am i doing wrong ?
On Battery shutdown behaviour is configured the following way:
On-Battery Shutdown Behavior

Thanks for any hint.
Bernd
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-17 11:11 PM

0 Likes
0
2993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-17 11:11 PM

Hi,

Did the NMC log receiving the shutdown command from the PCNS client? If so you should brain dead the UPS and then run the test again. 

See Schneider Electric FAQ FA156611 for assistance with the brain dead procedure. 

Reply

Link copied. Please paste this link to share this article on your social media post.

bernd_apc
Ensign bernd_apc
Ensign

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-15 06:16 AM

0 Likes
0
2994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:39 AM . Last Modified: ‎2024-03-15 06:16 AM

Hi Bill,

thanks for your message. It's working now. I choosed to start from the end. I configured "Low Battery Duration" with 20 minutes, now UPS will shutdown the servers when only 20 minutes of runtime are left. That does work properly, and also the outlets are turned off 20 minutes after beginn of shutdown.
I'm testing now if my server (HP Proliant ML 350) will boot automatically when the outlets are turned on again.

Bernd

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of