Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

server shut down, power and ups remained on?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • server shut down, power and ups remained on?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:18 PM . Last Modified: ‎2024-03-15 04:09 AM

0 Likes
3
949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:18 PM . Last Modified: ‎2024-03-15 04:09 AM

server shut down, power and ups remained on?

Smart UPS 2200, the server it was connected to lost power, when I went to check it out, the server was off, the UPS was on, replace battery light was solid red, battery charge lights were all green- full charge. I powered the server back on, replace battery still red and full charge sitll showing on the UPS.

questions- why did the server lose power, and do the batteries actually need replacing?
Also, server not using powerchute, and the ups is about 6 years old with original batteries.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:18 PM . Last Modified: ‎2024-03-15 04:09 AM

0 Likes
0
949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:18 PM . Last Modified: ‎2024-03-15 04:09 AM

Smart UPS 2200, the server it was connected to lost power, when I went to check it out, the server was off, the UPS was on, replace battery light was solid red, battery charge lights were all green- full charge. I powered the server back on, replace battery still red and full charge sitll showing on the UPS.

questions- why did the server lose power, and do the batteries actually need replacing?
Also, server not using powerchute, and the ups is about 6 years old with original batteries.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:18 PM . Last Modified: ‎2024-03-15 04:09 AM

0 Likes
0
949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:18 PM . Last Modified: ‎2024-03-15 04:09 AM

Thanks for the quick reply, I have ordered new batteries, I didn't notice a power flicker or anything that would cause it to go to battery, but it is definitely time to replace the batteries on it.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:18 PM . Last Modified: ‎2024-03-15 04:09 AM

0 Likes
0
949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:18 PM . Last Modified: ‎2024-03-15 04:09 AM

the battery likely needs replacement. typical life is 4 or 5 yrs. your server may have dropped if the UPS failed a self test (ie the UPS went to battery but no battery life remained - so the server dropped). Even though the battery is CHARGED all the way, its capacity is reduced over time until it needs replacement and the indicator illuminates.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:18 PM . Last Modified: ‎2024-03-15 04:09 AM

0 Likes
0
950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:18 PM . Last Modified: ‎2024-03-15 04:09 AM

Smart UPS 2200, the server it was connected to lost power, when I went to check it out, the server was off, the UPS was on, replace battery light was solid red, battery charge lights were all green- full charge. I powered the server back on, replace battery still red and full charge sitll showing on the UPS.

questions- why did the server lose power, and do the batteries actually need replacing?
Also, server not using powerchute, and the ups is about 6 years old with original batteries.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of