Just wanted to ask if anyone know the SSH commands to enable the alarm and setup the High/Max for both Temp/Humi and Sensor name via command line with SSH ?
Example model is AP8853
thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-06 05:40 AM
Hi,
If you run 'help' on the CLI these will all show under 'device commands'.
I believe you're looking for:
humAlGen / humLow / humMin
tempAlGen / tempHigh / tempMax
sensorName
most of these will report the current value if run alone, or set a value if a value is provided. You can use eg "help tempAlGen" for more detail.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-06 05:40 AM
Hi,
If you run 'help' on the CLI these will all show under 'device commands'.
I believe you're looking for:
humAlGen / humLow / humMin
tempAlGen / tempHigh / tempMax
sensorName
most of these will report the current value if run alone, or set a value if a value is provided. You can use eg "help tempAlGen" for more detail.