"UPS Not Found" using Network Management Card 2

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • "UPS Not Found" using Network Management Card 2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:32 AM . Last Modified: β€Ž2024-03-08 04:43 AM

0 Likes
11
5173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:32 AM . Last Modified: β€Ž2024-03-08 04:43 AM

"UPS Not Found" using Network Management Card 2

Hello,

We're having a problem getting one of our Smart UPS 3000 XL units to appear in the network management interface. I'm able to log into the network card and you can see(attached) what our homepage looks like. I believe this unit was configured before as it has a static IP and the person who performed the initial configuration would have noticed this problem. Right now, we have production equipment plugged into the unit. A midday hard-reboot will not be possible.

The network management card has been in use for about 3 weeks now.

I guess my questions are:

- Is there anything I can do to 'reset' the management card without wiping the network settings?
- Has anyone seen this issue before?
- Will resetting the network management interface affect any of the production equipment?

Message was edited by: danny8630

Added screen shots

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

0 Likes
0
5172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

ok great. thanks for the information. let us know if you need anything else.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:43 AM

0 Likes
0
5172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:43 AM

APC has issued an RMA for our case. Marking this thread as answered.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:43 AM

0 Likes
0
5172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:43 AM

Alright, so we were able to perform the Dead Braining procedure and reseated the NMC while it was powered off--however this did not help the problem. So, we then attempted to test with known good equipment from our other UPS. We took out the known GOOD NMC from the known GOOD UPS and placed it into the questionable UPS(while it was powered off) and tried to see if the problem was resolved. To our surprise, it wasn't.

I've deemed the UPS to be defective since a known good NMC does not read the UPS information. I will be contacting APC to process an RMA for warranty replacement.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

0 Likes
0
5173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

ok great. thanks for the information. let us know if you need anything else.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

0 Likes
0
5172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

After rebooting the NMC, there has been no change and the UPS is still not detected. Could the card be defective?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

0 Likes
0
5172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

can you try reseating the NMC in the smartslot? the issue could be the card or the slot on the UPS. personally, i'd suggest either a.) trying a different card in this slot or b.) try this card in a different UPS slot.

that should give us an idea on where the issue is, if not a definitive answer.

also, can you post the event.txt from the NMC for me? you can use these instructions -> http://nam-en.apc.com/app/answers/detail/a_id/9321

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

0 Likes
0
5172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

Will do--Can the card be replaced/reseated with the UPS powered on?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

0 Likes
0
5172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

well officially, you should power down the UPS and remove the attached load, referred to on the forum as the braindead process.

i personally have never done that and never had an issue. the risk vs. the downtime is not worth it to me and again, the risk is very slim. if you rather do that, i can outline the procedure for you but i'd just go for it.

also, clarkson mentioned to me to ask you if you had any other serial cables or smart slot accessories attached to this UPS that could be disrupting communication?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

0 Likes
0
5172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

No additional devices are plugged into the UPS--just the RJ45 cable into the Network Management Card.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

0 Likes
0
5172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

ok thanks. just wanted to confirm no other strange messages were present and that the NMC NEVER established communication with the UPS.

I would try a reseat first then try a different UPS or NMC based on the items suggested above (if you can). or at a minimum, try another accessory in the slot to narrow this down to NMC or UPS problem.

one last step may be to try and format the NMC which will wipe out all settings and logs (IP settings, etc). i can go over that with you if you cannot try any of the items above.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

0 Likes
0
5172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

Hmm---seems like the Smart UPS 3000XL only has one Accessory slot. It will be a challenging task, but we have a second 3000XL with the another NMC we can try.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

0 Likes
0
5172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:33 AM . Last Modified: β€Ž2024-03-08 04:42 AM

right, probably only has one but you can buy an external chassis, like [this one|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9600]. just checking πŸ™‚

let me know how you make out.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore