"Turn Off Delay" Query

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • "Turn Off Delay" Query
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
simonbrads_apc
Crewman simonbrads_apc
Crewman

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

0 Likes
5
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

"Turn Off Delay" Query

Hi all,

I'm finding some of the terminology used in the user manual for my UPS inconsistent and somewhat confusing, in particular, as related to the main and switched outlet groups. I have a Smart-UPS 1000VA LCD (SMT1000I).

The user manual mentions:

β€’ UPS outlets
β€’ Main group outlets
β€’ Switched outlets
β€’ Group 1 outlets

The term "UPS outlets" is only used in the "Customize the Main and Switched Outlet Groups" table. Does it mean the same as "main group outlets"? And am I right in thinking that "group 1 outlets" are the switched outlets? (Presumably, bigger units have "group 2 outlets" as well.)

The user manual lists the "Turn Off Delay" default settings as:

β€’ 0 sec (UPS Outlets)
β€’ 90 sec (Switched Outlet Groups)

However, there's only one "Turn Off Delay" setting (I think?), so how can the different groups have different delays?

As a test, I told my UPS to "turn off - use delay". Everything switched off after 90 seconds, so it looks like all my outputs are behaving as switched outlet groups. Maybe the point about "UPS Outlets" is an error in the doc, and doesn't relate to my UPS at all?

I've just realized that the main outlet group can't have a delay less than the switched groups, as this would violate the "master switch" property of the main group: the switched outlet group can only be on while the main group is on, right? (Unless the main group is told to switch off only after the switched groups are switched off, so the main group's delay is, in effect, added to the switched groups' delay?)

Sorry for asking such newbie questions, but I've read through the user manual several times, and I still don't quite get it. πŸ™‚

Thanks for any advice you can offer!

Cheers,
Simon

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

0 Likes
0
3452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

>
Sorry for asking such newbie questions, but I've read through the user manual several times, and I still don't quite get it. πŸ™‚
>

It's confusing -- I think you understand it better than most.

>
The term "UPS outlets" is only used in the "Customize the Main and Switched Outlet Groups" table. Does it mean the same as "main group outlets"? And am I right in thinking that "group 1 outlets" are the switched outlets? (Presumably, bigger units have "group 2 outlets" as well.)
>

--"UPS Outlets" refers to all UPS outlets, both main and switched.-- UPS Outlets refers to the main outlet group. Group 1 is the switched outlets, and yes, bigger units have group 2 as well.

>
The user manual lists the "Turn Off Delay" default settings as:

- 0 sec (UPS Outlets)
- 90 sec (Switched Outlet Groups)

However, there's only one "Turn Off Delay" setting (I think?), so how can the different groups have different delays?
>

The 0s delay might refer to older UPSes that don't have outlet groups, or the main outlet group.

>
...Unless the main group is told to switch off only after the switched groups are switched off, so the main group's delay is, in effect, added to the switched groups' delay?
>

Correct. Today, the off delay on the main outlet group starts only after the switched outlets have finished turning off.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

0 Likes
0
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

>
Sorry for asking such newbie questions, but I've read through the user manual several times, and I still don't quite get it. πŸ™‚
>

It's confusing -- I think you understand it better than most.

>
The term "UPS outlets" is only used in the "Customize the Main and Switched Outlet Groups" table. Does it mean the same as "main group outlets"? And am I right in thinking that "group 1 outlets" are the switched outlets? (Presumably, bigger units have "group 2 outlets" as well.)
>

--"UPS Outlets" refers to all UPS outlets, both main and switched.-- UPS Outlets refers to the main outlet group. Group 1 is the switched outlets, and yes, bigger units have group 2 as well.

>
The user manual lists the "Turn Off Delay" default settings as:

- 0 sec (UPS Outlets)
- 90 sec (Switched Outlet Groups)

However, there's only one "Turn Off Delay" setting (I think?), so how can the different groups have different delays?
>

The 0s delay might refer to older UPSes that don't have outlet groups, or the main outlet group.

>
...Unless the main group is told to switch off only after the switched groups are switched off, so the main group's delay is, in effect, added to the switched groups' delay?
>

Correct. Today, the off delay on the main outlet group starts only after the switched outlets have finished turning off.

Reply

Link copied. Please paste this link to share this article on your social media post.

simonbrads_apc
Crewman simonbrads_apc
Crewman

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

0 Likes
0
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

Thanks very much! With a little extra testing, and with the hints you provided, I've now got my head around the on/off delays (and also the load shedding options).

I do think the user manual could do with a once-over by a competent technical author, though. πŸ™‚ (e.g., "UPS outlets" is used in one place, without having been introduced; "main outlet group" and "main group outlets" both refer to the same thing; etc.) (I should admit that I'm quite pedantic, but I get to edit technical documents at work, and these are the sorts of things I pick up on. πŸ™‚ )

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

0 Likes
0
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

I think your comments about the user manual are accurate and perceptive.  To say that the manual could do with a once-over is a very kind. You are not being pedantic in this case, as the document is inconsistent, incomplete, and unnecessarily terse.  

I ran into another usage document that can help: "APC APPLICATION NOTE #165, Switched Outlet Groups on SMT and SMX Smart-UPS" By Neil Whiting, found at: www.apcmedia.com/salestools/NWHG-8SJN9A/NWHG-8SJN9A_R1_EN.pdf (also attached).  While this note gives some good examples of how the switched outlet groups can be used, it does not provide any help with how to use the LCD interface to configure the examples on a given UPS.  This is unfortunate, since for many users, the LCD interface will be their first experience, e.g., before they get the PowerChute software working.

Attachments
  • Tags:
  • manual
  • smart-ups
  • user
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

0 Likes
0
3453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

On 1/20/2012 11:35 AM, voidstar said:

--"UPS Outlets" refers to all UPS outlets, both main and switched.-- UPS Outlets refers to the main outlet group.

The above is confusing, as it defines "UPS Outlets" twice. When does "UPS Outlets" refer to all UPS outlets and when does it refer to the main outlet group?  

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

0 Likes
0
3454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:26 AM . Last Modified: β€Ž2024-03-11 02:37 AM

It's been a while since I wrote that so I'm not sure exactly what I meant. Looking over the UPSes I have access to, there's an SMT750 with a single Main Outlet Group called "UPS Outlets". In that case, main outlet group is also all of the UPS outlets.

I think it's difficult for the tech writers to describe how to use the switched outlets because their functionality isn't an exact match for the problems they're designed to solve. For example, if you want to stagger turn-on of the outlets to minimize inrush current on startup, you can set the turn on delays. But that same turn-on delay also applies when in-rush isn't an issue such as commanding a single outlet to turn on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.