"Battery Discharged" error is displayed after restarting the APC Symmetra RM

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • "Battery Discharged" error is displayed after restarting the APC Symmetra RM
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:07 AM

0 Likes
5
2825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:07 AM

"Battery Discharged" error is displayed after restarting the APC Symmetra RM

We bought two APC Symmetra RM (2 power modules and 7 batteries per each). We tested them 3 weeks ago and everythig was going fine. After that we stoped the APC, for maintenance reasons untill friday. When we started again, the following message was displayed: "Battery discharged". So I'm wondering if the batteries are destroyed or they are drained. What should I do to restart the system and to  charge the batteries, because I've let the UPS ON for half a day and the batteries are still discharged.

Thank you,

Stefan

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • error
  • power
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:03 AM . Last Modified: ‎2024-03-13 12:06 AM

0 Likes
0
2824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:03 AM . Last Modified: ‎2024-03-13 12:06 AM

Hi Stefan,

I am in the United States so I can't ship from here. Can you contact your local support and you can send them this thread if you need to so they could send an SYBT2 for you under goodwill. Also, we do that here in NAM and I can't speak for our EMEA support but I don't see why not if I say so laughing

Anyway, the part number is SYBT2 so I am not sure if you can request a quote through your reseller or ask EMEA support to do that as well. I don't want to give you the wrong pricing.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:07 AM

0 Likes
0
2824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:07 AM

Anytime you turn a Symmetra off and the batteries are not charging, you should disconnect the batteries from the frame (so pull them out a few inches at least) so they do not discharge into the frame over time which sounds like what happened here.

Can you confirm the current battery voltage on the system please? And is it running online or in bypass?

If its easier too, the logs from the pre-installed management card would be helpful. Instructions on downloading are in the knowledge base http://www.apc.com/site/support/index.cfm/faq/ in article ID FA156131. If the card is not configured, you can configure it as well and the logs will still be there.

Lastly, are these all brand new batteries? The first digits of the serial number on the batteries would be helpful i.e. QD1213XXXXX

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:07 AM

0 Likes
0
2824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:07 AM

Hi Angela,

The Symmetra was running online and the batteries are brand new.

Batteries info:

Model: SYBT2

S/N: 5D1246T00966

JPN: 885-669911

I've checked some information on the UPS:

DIAGS -> BATTS -> STATS:  0 of 6 bats        

  1. Bat 1 of 6
  2. Main Frame Module:
  •      Level 2 from top
  •      Status: Not Installed

Why the APC does not recognize the batteries?

I've attached the following files:

  • config.ini
  • data.txt
  • event.txt

Thank you for your help,

Stefan

Attachments
event.txt.zip
config.ini.zip
data.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:07 AM

0 Likes
0
2824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:02 AM . Last Modified: ‎2024-03-13 12:07 AM

Hi Stefan,

What do you mean the UPS was online? I guess what I mean is how was it turned off/on for maintenance? I see a lot of in bypass for maintenance in the log and coldstarts on the management card.

Anyway, the battery bus voltage is extremely low and that is why we cannot see any batteries and why the UPS cannot come online (since it does not appear to be per the log). So somehow, the batteries were left without being charged and have effectively been damaged. The nominal battery voltage on this system is ~137vDC and anything below ~95vDC will be a problem. Yours is at ~45vDC currently per the data log. Unfortunately, these batteries should be removed and discarded because if you get any new batteries, putting them in with the batteries that are of low voltage already will kill that new battery. You cannot mix a fresh battery with these that you have installed currently that are practically dead. They are so low that they will not be able to charge up.

So, I can't speak for technical support in your region but here, we would maybe make an exception and maybe provide you one good battery so you can bring the system online because in the log, it shows me the output power is turned off so your UPS is not online since it has no good batteries to run online. Then, you'd have to look into replacing the other batteries because we usually define this situation as negligence because the batteries were not stored properly while the UPS was down for maintenance.

Let me know if you have further questions. Sorry for the bad news here cry

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:03 AM . Last Modified: ‎2024-03-13 12:07 AM

0 Likes
0
2824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:03 AM . Last Modified: ‎2024-03-13 12:07 AM

Hi Angela,

In the previous post you said that you can provide us with a new battery for testing the UPS. Is the offer still available?

Our address is:

SC GARMIN CLUJ SRL

Street: SOMESULUI NR. 2-12, CLUJ-NAPOCA, ROMANIA

I have another question:

Can you send me an offer for 14 batteries?

Thank you,

Stefan

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:03 AM . Last Modified: ‎2024-03-13 12:06 AM

0 Likes
0
2825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:03 AM . Last Modified: ‎2024-03-13 12:06 AM

Hi Stefan,

I am in the United States so I can't ship from here. Can you contact your local support and you can send them this thread if you need to so they could send an SYBT2 for you under goodwill. Also, we do that here in NAM and I can't speak for our EMEA support but I don't see why not if I say so laughing

Anyway, the part number is SYBT2 so I am not sure if you can request a quote through your reseller or ask EMEA support to do that as well. I don't want to give you the wrong pricing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore