Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-29 06:14 AM . Last Modified: 2024-03-12 11:52 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:14 AM . Last Modified: 2024-03-12 11:52 PM
So, the other day I conducted a planned power shutdown in my data center. PCNS on physical servers worked perfectly to shut down their hosts and associated UPS. However, my virtual servers and hosts went through a hard shutdown when the UPS shut down. I found out later that this was due to a communication failure between the PCNS appliance and the vCenter server that had occurred several hours beforehand.
My question is, how can I be alerted when the PCNS appliance can't communicate with the vCenter server? I don't see anything related to that in the event configuration page.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:14 AM . Last Modified: 2024-03-12 11:51 PM
Hi,
I have entered an enhancement request to add lost communications with vCenter to be a configurable event. I do not have a date for the next release but the enhancement is on the list.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:14 AM . Last Modified: 2024-03-12 11:52 PM
Hi,
What version of PCNS are you running. If you are running PCNS 4.2 you can utilize SNMP to received notifications. If not you can script PCNS to send an e-mail alert. I know one of the other forum members Norman is scripting PCNS on Windows and Linux to e-mail alerts.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:14 AM . Last Modified: 2024-03-12 11:51 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:14 AM . Last Modified: 2024-03-12 11:51 PM
Thanks for the response, it is version 4.2. I could utilize SNMP, will it alert if PCNS loses connection to the vCenter server?
Since maintaining communication between vCenter and PCNS is critical (for the shutdown of VMs), is there any chance that APC will include this kind of alert in the next release?
Thanks,
Joe
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:14 AM . Last Modified: 2024-03-12 11:51 PM
Hi,
I have entered an enhancement request to add lost communications with vCenter to be a configurable event. I do not have a date for the next release but the enhancement is on the list.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.