possible issue with APC 7968 Switch PDU

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • possible issue with APC 7968 Switch PDU
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

0 Likes
1
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

possible issue with APC 7968 Switch PDU

We have set up an APC PDU Model # 7968
we ordered a 3phase 208V circuit 40amps each phase

we did this because our unit has a 35amps per phase, and we figured we can drive it up to 30 - 33 amps and we would block the breaker on the PDU before we tripped the breaker in the data center.

here is the issue - now we have it all configured, we have 17amps per Bank and the total on the PDU shows 20amps

did we miss calculate here on something?

any help please

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

0 Likes
0
655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

hmm, i am not an expert on three phase power but the electrical specifications sheet for this model (http://www.apcmedia.com/salestools/ASTE-6Z6K7J_R1_EN.pdf) indicates that it has an output current rating of - 15A/C13, 16A/C19; 16A/ bank. Thus, that's why the banks have 20A breakers on them.

i found some info that I have on a different PDU but I think it is the same explanation here:

In regards to the AP7998, each bank references two phases:

Bank 1 - Phase 1 and 3
Bank 2 - Phase 2 and 1
Bank 3 - Phase 2 and 3

The breaker on each bank is rated for 20 amps. Here is an explanation how the phases are distributed:

"Bank 1 draws current from phases 1 and 2 simultaneously. Bank 2 draws current from phases 2 and 3. This means that phase 2 is supplying current to both banks 1 and 2. However, like the phases, the banks are 120° out of phase. This means that part of the time that current is flowing one direction on bank 1, it is flowing the same direction on bank 2 and the two currents increase the draw from phase 2 to over 20 A. However, at other times, when current is flowing one direction on bank 1, it is being returned on bank 2. This means that you can't just add the loads on the two banks to get the load on phase 2.

Here is another way to look at it. We are in essence supplying three 120 V phases, but we are powering three 208 V loads. If the loads are 20 A, the total power consumed is ( 3 banks) x (208 Volts) x (20 Amperes) = 12480 Watts. The current on the input must then be (12480 Watts)/(three phases x 120 Volts) = 34.6 Amperes."

hope that helps!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

0 Likes
0
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:18 AM . Last Modified: ‎2024-03-18 02:32 AM

hmm, i am not an expert on three phase power but the electrical specifications sheet for this model (http://www.apcmedia.com/salestools/ASTE-6Z6K7J_R1_EN.pdf) indicates that it has an output current rating of - 15A/C13, 16A/C19; 16A/ bank. Thus, that's why the banks have 20A breakers on them.

i found some info that I have on a different PDU but I think it is the same explanation here:

In regards to the AP7998, each bank references two phases:

Bank 1 - Phase 1 and 3
Bank 2 - Phase 2 and 1
Bank 3 - Phase 2 and 3

The breaker on each bank is rated for 20 amps. Here is an explanation how the phases are distributed:

"Bank 1 draws current from phases 1 and 2 simultaneously. Bank 2 draws current from phases 2 and 3. This means that phase 2 is supplying current to both banks 1 and 2. However, like the phases, the banks are 120° out of phase. This means that part of the time that current is flowing one direction on bank 1, it is flowing the same direction on bank 2 and the two currents increase the draw from phase 2 to over 20 A. However, at other times, when current is flowing one direction on bank 1, it is being returned on bank 2. This means that you can't just add the loads on the two banks to get the load on phase 2.

Here is another way to look at it. We are in essence supplying three 120 V phases, but we are powering three 208 V loads. If the loads are 20 A, the total power consumed is ( 3 banks) x (208 Volts) x (20 Amperes) = 12480 Watts. The current on the input must then be (12480 Watts)/(three phases x 120 Volts) = 34.6 Amperes."

hope that helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore