pcnsconfig.ini error/warning in event log with PCNS 4.4

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • pcnsconfig.ini error/warning in event log with PCNS 4.4
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
118
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
pgpc_apc
Crewman pgpc_apc
Crewman

Posted: ‎2021-06-30 06:11 AM . Last Modified: ‎2024-03-08 01:27 AM

0 Likes
2
7498
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:11 AM . Last Modified: ‎2024-03-08 01:27 AM

pcnsconfig.ini error/warning in event log with PCNS 4.4

On each reboot of a Win 2019 server or restart of the pcns service, pcns 4.4 logs the following error twice:

ERROR: The ini file is missing shutdownCommandFile key from section Shutdown

Adding the empty key "shutdownCommmandFile = " to the Shutdown section in psnconfig.ini causes the error to be replaced by a warning:

WARNING: The invalid key shutdownCommandFile should be deleted from section Shutdown in the ini file

We are running pcns 4.2 on a Win 2008 server, which has an empty shutdownCommandFile = key in its pcnsconfig.ini, file and it does not give the warning it its event log.  There is nothing in the "PowerChute Configuration File - Using pcnsconfig.ini" manual that explains why the error/warning is being generated or, more importantly, how to get rid of it.

Any help in eliminating the error/warning messages would be appreciated.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:11 AM . Last Modified: ‎2024-03-08 01:27 AM

0 Likes
0
7489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:11 AM . Last Modified: ‎2024-03-08 01:27 AM

Hi,

Sorry for the inconvenience. That is a know issue as listed in the PCNS 4.4 release notes (see atteched PDF). 

To resolve the issue add the line shutdownCommandFile = to the pcnsconfig.ini file [shutdown] section 

[Shutdown]
shutdownCommandFile =

Do Not include the quotes as shown in the release notes. If the quotes are added you will see the warning. 

WARNING: The invalid key shutdownCommandFile should be deleted from section Shutdown in the ini file

 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:11 AM . Last Modified: ‎2024-03-08 01:27 AM

0 Likes
0
7490
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:11 AM . Last Modified: ‎2024-03-08 01:27 AM

Hi,

Sorry for the inconvenience. That is a know issue as listed in the PCNS 4.4 release notes (see atteched PDF). 

To resolve the issue add the line shutdownCommandFile = to the pcnsconfig.ini file [shutdown] section 

[Shutdown]
shutdownCommandFile =

Do Not include the quotes as shown in the release notes. If the quotes are added you will see the warning. 

WARNING: The invalid key shutdownCommandFile should be deleted from section Shutdown in the ini file

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Momo-70
Crewman Momo-70
Crewman

Posted: ‎2023-02-02 10:30 AM

0 Likes
0
3861
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-02 10:30 AM

Hi,

 

I am running PCNS 4.4.3 VMWare Appliance.

I am running it on a VMWare ESXI 8.0 Host.
I am aware that in the PCNS Manual it says that it isnt officially supported on anything higher than VMWare ESXI 7.0, but we already had ESXI 8.0 with new servers in place, before buying the APC UPS, so I have run the PCNS VM Appliance up on it anyway, as I didn't have much choice.

It is actually working fine on the ESXI 8.0, the only issue I have is that in the Event Log I get the following error message:

ERROR: The ini file is missing shutdownCommandFile key from section Shutdown

 

I am aware that it is a known issue in the release notes and I have added the "shutdownCommandFile =" to the shutdown section of pcnsconfig.ini.

Now when I add the line into the ini file and reboot the VM, the error message no longer appears in the Event Log.

However what has been happening, is that for some unknown reason, the "shutdownCommandFile = " line that I add gets removed/deleted from the pcnsconfig.ini by itself at some unknown point, whilst the PCNS VM Appliance is running, and then when the VM is restarted again, the error msg reappears in the Event Log again.

 

I have tried adding the "shutdownCommandFile =" line to both the pcnsconfig.ini and the pcnsconfig_backup.ini, but the same happens to both files and the "shutdownCommandFile =" is removed/deleted from both files at some unknown point, and the error msg reappears in the Event Log whenever the VM is restarted.

Whilst the PCNS VM Appliance is continually running and never shutdown/restarted, after adding in the "shutdownCommandFile =" line and starting it backup, the Error msg doesn't appear in the log.
Once restarted the error msg returns and when I check the "shutdownCommandFile =" is gone from the pcnsconfig & backup ini files.

I have also stopped the PowerChute service after the VM appliance has been running for a while, with no error msg in the Event Log and have checked the pcnsconfig * backup files and the "shutdownCommandFile =" is gone.

Does anyone know what is causing this line to be removed/deleted from the ini files on its own, as having to continually add it back in every time I restart the VM appliance is just frustrating?

 

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of