noob Q on UPS communication

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • noob Q on UPS communication
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

0 Likes
5
1261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

noob Q on UPS communication

Hi

We have been using a Smart-UPS 1500 for several years. It is quite obvious that the device is intended to regulate normal power and supply battery power during a mains power failure to several devices (it has 4 power sockets). However, there is only one communication port available.

What are you supposed to do when you have more than one server attached to the device? When battery power is due to fail the scheduled shutdown sequence will allow one server, the one that is connected to the UPS via the communication port to shutdown gracefully.

I can't see anything in the documentation that came with the UPS to explain how this can be achieved. Anyone know how this can be done?

For the most part we have been lucky in that the majority of power outages have been covered by the remaining battery time and power to the servers has remained uninterupted. I don't want to push my luck, though.

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

0 Likes
0
1261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

Thanks a lot.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

0 Likes
0
1261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

Depending on the type of UPS, you have a few options.

  • For any Smart UPS, the easiest and most cost effective option is to use a UPS Network Management Card installed in the SmartSlot of the UPS and install PowerChute Network Shutdown on any clients attached to the UPS. The UPS Network Management Card talks to the PowerChute software on your servers via the network and keeps them updated on the UPS status. Based on options that you configure, you can determine when to shut all or some of the clients down to stagger the shutdowns. This is nice because it uses your existing network connections, presuming they are present, and then you get all the other bells and whistles of the Network Management Card product. This does not work though on SMC/SC products.

  • For older Smart UPS that have a DB-9 style serial port, we offered a serial expander option in 2 or 7 port models that provided more serial ports for the UPS. This required lots of extra serial cables and provided "basic" or "simple" shutdown for 6 of the clients and then one "advanced" port which is what your UPS has available. You then install PowerChute Business Edition in simple signaling mode on the clients to interpret the signaling over the serial cable. With the one client on the advanced port, this client can change settings on the UPS, view status information, etc because simple signaling clients cannot do that. Smart signaling refers to two way communication between UPS and computer/client and simple is one way voltage signals from the UPS to client/computer. This can get expensive and messy with the cables and is pretty much a legacy solution that I would not recommend unless doing the first option for some reason. This is also not supported on newer UPSs with the prefix SMT/SMX or SMC either.

If you give me the exact model of the UPS from the white sticker, I can verify the options. Hope this helps.

P.S. - if you decide on a Network Management Card, one of our users here stevejenkins was nice enough to put a blog together with some helpful information -> HowTo: Configure Low Battery Duration and PCNS to Shut Down with an APC SmartUPS | Steve Jenkins' Bl...

So, the Network Management Card is the most flexible and easiest option for any Smart UPS really.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

0 Likes
0
1261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

Mark:

+1 to everything Angela said. Hopefully you have the same SmartUPS 1500 that I do -- with a "Smart Slot" in the rear of the device. If that's the case, then grab a used AP9617 Network Management Card on eBay for cheap, then do as Angela suggests. smile She's absolutely right: the NMC is indeed the most flexible and easiest option for any SmartUPS. You're not getting anywhere NEAR the potential performance from your UPS without one!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

0 Likes
0
1261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

Thanks a lot to both of you for your very helpful replies.

The rear of the device has a USB and serial port. The model number is: DLA1500RMI2U

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

0 Likes
0
1261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

Ok, so you can only use USB OR serial on that device, not both.

Your UPS will support both a Network Management Card (UPS Network Power Management Cards – Remote Monitoring | APC) OR the Serial Interface Expander options (Interface Expanders – Additional UPS Management Cards | APC).

Please note AP9617/18/19 will work for UPS Network Management Cards but they are an older platform and are not currently developed on for bug fixing and new features. AP9630/31 is the current offering.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

0 Likes
0
1262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:06 AM . Last Modified: ‎2024-03-12 04:45 AM

Thanks a lot.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore