i tried to set up the network shutdown with the 3 up's at first only 1 and 3 could connect so i reset the authentication phrase on all 3 to be admin user phrase
after that i could connect to 2 but not 1 and 3
ive reset the authentication phrase dozens of times to different things, and rebooted the management interface but i cant get it to work.
ive used different browsers, IE AND chrome, still not working. any idea what im doing wrong?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:31 PM . Last Modified: 2024-03-06 10:54 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:31 PM . Last Modified: 2024-03-06 10:54 PM
I resolved this by changing the user passphrase to something without spaces in it. as apparently it doesn't like that.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:31 PM . Last Modified: 2024-03-06 10:54 PM
Hi,
Is PowerChute installed and showing no communications with the 2 NMCs and if so on what OS PCNS is installed on? Also, what is the firmware revision running on the NMCs?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:31 PM . Last Modified: 2024-03-06 10:54 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:31 PM . Last Modified: 2024-03-06 10:54 PM
I resolved this by changing the user passphrase to something without spaces in it. as apparently it doesn't like that.
Link copied. Please paste this link to share this article on your social media post.