error inverter ups

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
Andre_lopes_apc
Cadet
0 Likes
3
437

error inverter ups

This was originally posted on APC forums on 1/6/2016


Good morning, I have a UPS here with LED X access and two LED battery indicator access however it does not work

This being the sequence can of leds

0

1

1

0

0

What should I do?
I need that equipment

Tags (2)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
437

Re: error inverter ups

This reply was originally posted by Tuyishimire on APC forums on 1/15/2016


I have a same problem here, i changed batteries for a working unit but still no changes. what should we do next?

See Answer In Context

3 Replies 3
mitsmith_apc
Lt. Commander
Lt. Commander
0 Likes
0
439

Re: error inverter ups

This was originally posted on APC forums on 1/6/2016


Hi Andre,

This fault a lot of times points to bad batteries. How old is the unit and the batteries? Is the unit still powering your equipment?  I would use a volt meter to check the voltage of the batteries. Just measure the DC voltage at the anderson connector for each of the modules. When fully charged they should be 110 volts each. Do you have another unit that uses the same batteries? If so you could temporarily borrow those.

Andre_lopes_apc
Cadet
0 Likes
0
439

Re: error inverter ups

This was originally posted on APC forums on 1/7/2016


Was placed second battery of new modules and both with a DC voltage of 108V
PERSISTS EVEN SO THE DEFECT

BillP
Administrator Administrator
Administrator
0 Likes
0
438

Re: error inverter ups

This reply was originally posted by Tuyishimire on APC forums on 1/15/2016


I have a same problem here, i changed batteries for a working unit but still no changes. what should we do next?