Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-31 06:49 PM
I have a Smart-UPS 1000 XL with a management card(AP9617).
Recently ,it reports Discharged Battery error. I have replaced the batteries, but the error still exists.
Is any well-wisher willing to send me a copy of instruction about adjusting the UPS battery constants via serial cable?
My E-mail is radiumliu@gmail.com
Thanks a lot
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-02 06:14 AM
This and several other YouTube videos will provide you some insight:
https://youtu.be/YQi0lxkTxdM?si=Am1BLtnsLuglY-EP
A user manual for a similar model UPS and the command structure:
blob:https://www.apc.com/ae80c6b2-2231-4e71-9b75-768b41a26a97
I would suggest you begin with resetting the battery installation date. Than initiate a manual self test. If the self test completes successfully initiate a battery calibration with at least 30% attached load.
Once complete let the battery recharge and report back what you see and observe.
If the above steps fail you may consider completing a Brain Dead reset. Doing so will clear and reset the internal EEPROM.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-02 06:14 AM
This and several other YouTube videos will provide you some insight:
https://youtu.be/YQi0lxkTxdM?si=Am1BLtnsLuglY-EP
A user manual for a similar model UPS and the command structure:
blob:https://www.apc.com/ae80c6b2-2231-4e71-9b75-768b41a26a97
I would suggest you begin with resetting the battery installation date. Than initiate a manual self test. If the self test completes successfully initiate a battery calibration with at least 30% attached load.
Once complete let the battery recharge and report back what you see and observe.
If the above steps fail you may consider completing a Brain Dead reset. Doing so will clear and reset the internal EEPROM.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-02 08:15 PM
Thank you.
I repaired it with apcfix.exe.