dead UPS (SUA3000RMI2U)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • dead UPS (SUA3000RMI2U)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:36 AM . Last Modified: ‎2024-03-18 11:07 PM

0 Likes
6
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:36 AM . Last Modified: ‎2024-03-18 11:07 PM

dead UPS (SUA3000RMI2U)

Hi, i have received  a  SUA2200RMI2U for free. It has not been connected to a mains outlet (utility power) for 2-3 years, and all the battery is 0V.

My question.
Is there a way to get is to power up without battery connected, so i can  get an indication that it should be working when new battery's  is added. There is no feedback (LED or sound) from the UPS when connected to 230 V AC

Not to happy with  buying  battery's  for 200-300 €, if it is broken

Best
Ivan

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 0v
  • battery
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 02:37 AM . Last Modified: ‎2024-03-18 11:07 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:37 AM . Last Modified: ‎2024-03-18 11:07 PM

Thanks Mike - this was important in that I'm supporting a user that plugged in a SUA3000 (RM slim unit) without any batteries and expected it to operate.  I told him that he must have a good battery pack of 8 - 5.5AH batteries wired properly and connected for the unit to operate correctly.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:36 AM . Last Modified: ‎2024-03-18 11:07 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:36 AM . Last Modified: ‎2024-03-18 11:07 PM

Dear sir i have 2 apc RT-6000 UPS with APC ATS these two UPS are getting input voltage from ATS where ATS giving output to other devices in my server room like , Servers, switches, routers etc. as recently we have changed ups batteries and still showing error "UPS batteries Discharge" also on ATS i have selected preferred source to None and sensitivity level high and frequency deviation to wide. 

issues are as below

1. when main power shifts to generator it show event "battery discharge"

2. Showing 100% load on one UPS -A blinking all 5 batteries light on front panel of UPS _A  also showing error                          "battery soon exhausted" 

3. on UPS B event occurred continuously "Battery "discharge condition"

as discussed above i have installed new batteries and set frequency sensitivity level from low to medium and to high prefered source to A or B and None , frequency deviation level from wide , medium etc after dowing all things i have still recieving above discuss events

kindly resolve my issue as all data center is at risk please... 

  • Tags:
  • batteries
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:37 AM . Last Modified: ‎2024-03-18 11:07 PM

0 Likes
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:37 AM . Last Modified: ‎2024-03-18 11:07 PM

Ivan,

The SUA product line is designed to turn on without good batteries in the unit.  If you are getting no signs of life when the unit is properly plugged into mains, the unit may be bad and it is probably not worth investing in new batteries for this unit.

I would suggest completely removing the batteries from the unit, unplugging the unit from mains, holding the off button for about 20 seconds, plugging the unit back into mains, and try booting the unit up while looking for any sign of life.

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:37 AM . Last Modified: ‎2024-03-18 11:07 PM

0 Likes
0
1451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:37 AM . Last Modified: ‎2024-03-18 11:07 PM

Hi Jordan

I have now replaced the batteries, and it works again. 🙂

The firmware are from 2004, is there a more resent version i should use

 Model:  Smart-UPS 3000 RM
 Firmware Revision:  666.4.I
 Manufacture Date:  02/24/04
 Serial Number:  YS0409120602

Best regards
Ivan

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 02:37 AM . Last Modified: ‎2024-03-18 11:07 PM

0 Likes
0
1451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:37 AM . Last Modified: ‎2024-03-18 11:07 PM

Jordan;

I was not aware that SUA3000RM(XLs) units would show any signs of life with the battery pack disconnected - when connecting to AC power.  I recall that has been my experience (although I must admit it could be a SURT or other style unit - or that a relay might have "clicked", but that was about it).  Once a battery pack is connected that has some level of energy, the units have always tried to light up - usually go all the way to the battery check and then fail on bad batteries - if deficient batteries.  In all cases (dozens), good batteries resolved all the issues.  There have been times when one bad battery in the series "pack" was the culprit - and can happen with "new" batteries.

Can this be clarified?

Reply

Link copied. Please paste this link to share this article on your social media post.

mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-28 02:37 AM . Last Modified: ‎2024-03-18 11:07 PM

0 Likes
0
1451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:37 AM . Last Modified: ‎2024-03-18 11:07 PM

Hi Mark,

Jordan was mistaken. Please see our knowledge base below under the resolution section, number 1. 

http://www.schneider-electric.us/sites/us/en/support/faq/faq_main.page?page=content&country=US〈=en&id=FA156604

The SMX/SMT series will turn on without the battery. All other line interactive smart-ups will not.
For the double online smarts only our new SRT and the SURT15/20KVA will turn on without a battery.

Sorry for the original misinformation.

-Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 02:37 AM . Last Modified: ‎2024-03-18 11:07 PM

0 Likes
0
1453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:37 AM . Last Modified: ‎2024-03-18 11:07 PM

Thanks Mike - this was important in that I'm supporting a user that plugged in a SUA3000 (RM slim unit) without any batteries and expected it to operate.  I told him that he must have a good battery pack of 8 - 5.5AH batteries wired properly and connected for the unit to operate correctly.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of