can't web login to AP8841

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • can't web login to AP8841
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:03 AM . Last Modified: ‎2024-03-18 02:51 AM

0 Likes
5
1787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:03 AM . Last Modified: ‎2024-03-18 02:51 AM

can't web login to AP8841

I have an AP8841. When I attempt to access web console, I get message

ERROR: The application was not able to load
You are attempting to access an APC device.
There was a problem loading the application. please login to telnet for more details.

So I telnet into the device. It's not obvious what's wrong.
Other threads in this forum suggest maybe firmware needs updating. However it looks like I have latest stuff. About gives me this:

American Power Conversion Network Management Card AOS v5.1.2
(c) Copyright 2009 All Rights Reserved RPDU 2g v5.1.0
-------------------------------------------------------------------------------
Name : Unknown Date : 03/27/2011
Contact : Unknown Time : 21:52:26
Location : Unknown User : Administrator
Up Time : 0 Days 0 Hours 4 Minutes Stat : P+ N4+ N6+ A$


Type ? for command listing
Use tcpip command for IP address(-i), subnet(-s), and gateway(-g)

apc>about
E000: Success
Hardware Factory
---------------
Model Number: AP8841
Serial Number: ZA1051026106
Hardware Revision: 02
Manufacture Date: 12/18/2010
MAC Address: 00 C0 B7 55 6F C8
Management Uptime: 0 Days 0 Hours 4 Minutes

Network Management Card
---------------
Model Number: AP9537
Serial Number: ZA1051010554
Hardware Revision: 05
Manufacture Date: 12/15/2010

Application Module
---------------
Name: rpdu2g
Version: v5.1.0
Date: Apr 14 2010
Time: 14:50:01

APC OS(AOS)
---------------
Name: aos
Version: v5.1.2
Date: Apr 5 2010
Time: 14:03:27

APC Boot Monitor
---------------
Name: bootmon
Version: v1.0.2
Date: Jan 21 2010
Time: 13:35:57

apc>

I'm also confused because this was working fine when we first got the unit, and we've made no firmware upgrades or other changes to the unit.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:04 AM . Last Modified: ‎2024-03-18 02:50 AM

0 Likes
0
1787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:04 AM . Last Modified: ‎2024-03-18 02:50 AM

I had the same issue.

reinstalling the firmware using the upgrade utility worked for me as well.

Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:03 AM . Last Modified: ‎2024-03-18 02:51 AM

0 Likes
0
1787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:03 AM . Last Modified: ‎2024-03-18 02:51 AM

great. and yes, all three files are generally required.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:03 AM . Last Modified: ‎2024-03-18 02:51 AM

0 Likes
0
1787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:03 AM . Last Modified: ‎2024-03-18 02:51 AM

eventlog gives the following response:

E100: Command Failed
Event Log Not Available

I only have access to this system from a linux box. Was there some way that I can update firmware images simply by ftp'ing them to the IP address or something like that?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:03 AM . Last Modified: ‎2024-03-18 02:51 AM

0 Likes
0
1787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:03 AM . Last Modified: ‎2024-03-18 02:51 AM

I ftp'd the apc_hw05_aos_512.bin file to the PDU and I believe it accepted it, because it closed the ftp and when I logged in again it said uptime of 1 minute.
Also the status has changed from A$ to A- Still can't get in via web and eventlog is still unavailable.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:03 AM . Last Modified: ‎2024-03-18 02:50 AM

0 Likes
0
1787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:03 AM . Last Modified: ‎2024-03-18 02:50 AM

flashing all 3 files seems to have fixed it!!
Thanks!!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:04 AM . Last Modified: ‎2024-03-18 02:50 AM

0 Likes
0
1788
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:04 AM . Last Modified: ‎2024-03-18 02:50 AM

I had the same issue.

reinstalling the firmware using the upgrade utility worked for me as well.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore