can't establish hyperterminal communication with apc smart ups 5000 rt

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • can't establish hyperterminal communication with apc smart ups 5000 rt
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:44 PM . Last Modified: ‎2024-03-14 11:45 PM

0 Likes
3
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:44 PM . Last Modified: ‎2024-03-14 11:45 PM

can't establish hyperterminal communication with apc smart ups 5000 rt

Hello,

I have brand new APC Smart UPS 5000 RT and I am trying to connect to it with hyperterminal. I have used settings 2400 bps, N, 8, 1, no flow control. But after pressing enter I dont get any response from ups.
I tested on my windows notebook and another computer with linux minicom as well without success.
What could be the problem ?
There is network interface on the UPS as well, can I use it to connect to UPS ? What is the default IP address ?

Thank you !

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:44 PM . Last Modified: ‎2024-03-14 11:45 PM

0 Likes
0
2237
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:44 PM . Last Modified: ‎2024-03-14 11:45 PM

Thank you for the post. It helps me very much 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:44 PM . Last Modified: ‎2024-03-14 11:45 PM

0 Likes
0
2237
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:44 PM . Last Modified: ‎2024-03-14 11:45 PM

can you please confirm the exact model number on the UPS?

SURT5000XLT/SURT5000XLI uses a DB-9 connector on the back of it for communication and you need the cable part number of 940-0024 or 940-1524 to establish the connection. it is a DB-9 to DB-9 cable. the port settings on that are those that you tried: 2400 bps, N, 8, 1, no flow control. it wont work though if you arent using the APC cable I mentioned.

if the unit is a SURTD5000XLT /SURTD5000XLI (notice the D in the part number), then the communication port you need to be plugging into is RJ-45 and I believe it is labeled "communication" or "serial." It is NOT the one located on the actual network management card (AP9617, AP9618, or AP9619). the cable required for this is a 940-1525A cable and is RJ-45 to DB9. The port settings for this unit are different and it uses a baud rate of 9600. the rest of the settings are the same: 9600 bps, N, 8, 1, no flow control.

you will want to make sure the status lights on the network management card are lit up too for status and link.

by default, the network management cards are set up for DHCP/BOOTP but also require option 43 (which is a vendor cookie) to be set up on the DHCP/BOOTP server before it will accept the address. this is an option you can disable once you gain access to the card if you'd like.

[check this article out on the different ways to configure the NMC|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=3061]

hope that helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:44 PM . Last Modified: ‎2024-03-14 11:45 PM

0 Likes
0
2237
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:44 PM . Last Modified: ‎2024-03-14 11:45 PM

My model is SURTD5000XL so I changed the speed to 9600 and the communication is working now.
I got user name prompt.
Thank you !

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:44 PM . Last Modified: ‎2024-03-14 11:45 PM

0 Likes
0
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:44 PM . Last Modified: ‎2024-03-14 11:45 PM

Thank you for the post. It helps me very much 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore