apc smart-ups 900i calibration

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • apc smart-ups 900i calibration
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:08 AM . Last Modified: ‎2024-03-08 04:55 AM

0 Likes
3
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:08 AM . Last Modified: ‎2024-03-08 04:55 AM

apc smart-ups 900i calibration

I have an old apc smart-ups 900i, it's a 2nd generation ups. I need some help on using hyperterminal, the unit input is 230v, but it shows only 118v in the hyperterminal. It seems that the firmware or something is configured in 110v instead of 230v. I must have mess-up on the hyperterminal, I just dont remember. Thanks for the help.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:09 AM . Last Modified: ‎2024-03-08 04:54 AM

0 Likes
0
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:09 AM . Last Modified: ‎2024-03-08 04:54 AM

I was in hyperterminal, i was trying to change the "u" which is the upper transfer voltage to 264v.. i press "+" then after that the unit restarted and it can't go on battery mode during initialization or self-test, i found out the "B" which is the battery voltage went to "000.0" so i changed it to 24, self-test is already ok but i can't changed back the "u" to it's original value. reading of "u" is already 118v, and it cant go further than that.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:08 AM . Last Modified: ‎2024-03-08 04:55 AM

0 Likes
0
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:08 AM . Last Modified: ‎2024-03-08 04:55 AM

Why do you think it is like this? I am using fluke true-rms tester, the output of the UPS is 218 but in the hyperterminal it reads 115V.. My friend said that the firmware is 115V, which should be 230V in the first place.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:09 AM . Last Modified: ‎2024-03-08 04:54 AM

0 Likes
0
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:09 AM . Last Modified: ‎2024-03-08 04:54 AM

it probably is an issue with the firmware if you know that you went into hyperterminal and adjusted settings, then logged out, and noticed the change.

what exactly did you do before and after noticing this so we can track where the issue is?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:09 AM . Last Modified: ‎2024-03-08 04:54 AM

0 Likes
0
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:09 AM . Last Modified: ‎2024-03-08 04:54 AM

I was in hyperterminal, i was trying to change the "u" which is the upper transfer voltage to 264v.. i press "+" then after that the unit restarted and it can't go on battery mode during initialization or self-test, i found out the "B" which is the battery voltage went to "000.0" so i changed it to 24, self-test is already ok but i can't changed back the "u" to it's original value. reading of "u" is already 118v, and it cant go further than that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of