Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: ‎2021-07-09 04:15 AM . Last Modified: ‎2024-02-14 11:07 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-07-09 04:15 AM . Last Modified: ‎2024-02-14 11:07 PM
Hi
I have googled, to try find out what OID, i should use, to monitoring a AP7723 Current load.-
In the web interface i can see the load is now 5AMP, but witch OID in SNMP should i used to see this number to SNMP?
Hope someone can help me.
Thx.
Regards Kenneth Dalbjerg
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-07-09 04:15 AM . Last Modified: ‎2024-02-14 11:07 PM
Hi Kenneth,
Please look at the following OID in the APC PowerNet MIB: .1.3.6.1.4.1.318.1.1.8.5.4.3.1.4 (.iso.org.dod.internet.private.enterprises.apc.products.hardware.automaticTransferSwitch.atsStatus.atsStatusOutput.atsOutputPhaseTable.atsOutputPhaseEntry.atsOutputCurrent)
I used a MIB browser which is helpful to see all of the OIDs available, especially if you may be interested in other OIDs like the output VA.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-07-09 04:15 AM . Last Modified: ‎2024-02-14 11:07 PM
Hi Kenneth,
Please look at the following OID in the APC PowerNet MIB: .1.3.6.1.4.1.318.1.1.8.5.4.3.1.4 (.iso.org.dod.internet.private.enterprises.apc.products.hardware.automaticTransferSwitch.atsStatus.atsStatusOutput.atsOutputPhaseTable.atsOutputPhaseEntry.atsOutputCurrent)
I used a MIB browser which is helpful to see all of the OIDs available, especially if you may be interested in other OIDs like the output VA.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:07 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:07 PM
Thank you. I also think it was this one, but it response, was ten time high, than it should be.
Just google it, and it says it gives the status in milli amps 🙂
Again thanks for you help