AP7723: Phase Leds/Push-button hardware failure and initialized?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP7723: Phase Leds/Push-button hardware failure and initialized?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:07 PM

0 Likes
4
2409
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:07 PM

AP7723: Phase Leds/Push-button hardware failure and initialized?

Hello,

I got this error this weekend. What should I do? I have the AP7723 installed in a rack.

Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.

Automatic Transfer Switch: Phase Leds/Push-button hardware failure

 

 

Sincerly

 

Geir

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:07 PM

0 Likes
0
2405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:07 PM

01.05.2017 21:50:14 System: Web user 'admin' logged in from 10.xx.xx.xx

30.04.2017

01:11:34 Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
30.04.2017 01:11:34 Automatic Transfer Switch: Phase Leds/Push-button hardware failure.
29.04.2017 17:14:12 Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
29.04.2017 17:14:12 Automatic Transfer Switch: Phase Leds/Push-button hardware failure.
23.04.2017 01:00:52 System: Set Daylight Saving Time.
23.04.2017 01:00:52 System: Set Date or Time.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:07 PM

0 Likes
0
2405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:07 PM

Hi Geir,

Could you please post the full event.txt from your AP7723 ATS? You can obtain the .txt version of the log following instructions outlined here -> http://www.apc.com/us/en/faqs/FA156131

Worst case scenario, can you launch the event log in a new window through web UI and PDF it so we can see the log in its entirety? Just make sure there are no filters applied if you have to use this method to get the log.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:07 PM

0 Likes
0
2406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:07 PM

01.05.2017 21:50:14 System: Web user 'admin' logged in from 10.xx.xx.xx

30.04.2017

01:11:34 Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
30.04.2017 01:11:34 Automatic Transfer Switch: Phase Leds/Push-button hardware failure.
29.04.2017 17:14:12 Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
29.04.2017 17:14:12 Automatic Transfer Switch: Phase Leds/Push-button hardware failure.
23.04.2017 01:00:52 System: Set Daylight Saving Time.
23.04.2017 01:00:52 System: Set Date or Time.
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:06 PM

0 Likes
0
2405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:06 PM

Seems like everything is running fine, so I guess its not any problem? 🙂

 

Thanks for the quick respons.

Sincerly

 

Geir

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:06 PM

0 Likes
0
2405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-09 04:16 AM . Last Modified: ‎2024-02-14 11:06 PM

Hi Geir,

Yes, it looked like it recovered from failure and later initialized. I'd keep an eye on it. If it continues to do that a lot, then let us know and show the full log so we can see some back history and see if the problem is getting worse.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of