all my links to powerchute bad/ need to download powerchute for Win. 7, 64 bit APC smart SMT1500

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • all my links to powerchute bad/ need to download powerchute for Win. 7, 64 bit APC smart SMT1500
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
4
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

all my links to powerchute bad/ need to download powerchute for Win. 7, 64 bit APC smart SMT1500

I'm all confused.  I guess I didn't set up powerchute on this computer and all my web links to where I'd go to set up everything are not good.

I have APC smart  SMT1500, and just need powerchute download, I think. I've completely forgotten how to then get to webportal for me.

The IP address doesn't work anymore for me.

I'm completely at a loss, starting over completely.

And I can't log in to the APC main site where I registered.  My email they don't recognize so I can't reset my password, and get to my registered APC smart  SMT1500.

I'm not having a good day.

Thanks for your help and guidance.

OK, Edit----

I do have Powerchute on this computer, I updated it.  But the wizard didn't come up to configure at the webportal and all the links I have don't work.  Did the links/ IP change?  

The portal I show it should be is 6547  with my PC name before it.  I've tried this IP address http://127.0.0.1    that doesn't work wiht or without the port #.  

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

Thanks so much for the detailed information.
I did the command prompt sequence, and it showed stopped. but when I tried to start it said denied.  I am logged in as admin, which is myself.
I think I'll have to uninstall and reinstall.
Business Powerchute business edition,   installed.  
-----
So I uninstalled and reinstalled.  And that worked.  My links sort of work, and gets me where to I can make settings.
I also installed the Console, but I'm thinking you also have to have the server setup to use the console, cause I couldn't log in with my user name I just made.
But at least I can get to the website now and check and make settings so I will have the shutdown when we have a power outage, which we do often here.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

Hi,

Launch a web browser on the system running PowerChute and enter https://127.0.0.1:6547 You should be able to log into the PowerChute Agent. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

Hi Bill,

I've tried that, but it doesn't work. 

I've gone to the program list and clicked on the Agent Web Interface, but that doesn't work either.

I do have PowerChute installed, I updated it.

I used to be able to get there from that IP address.

I'm wondering if I should uninstall and reinstall at this point.

I've tried from Chrome and I.E.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

Hi,

Do you have PowerChute Business Edition or PowerChute Network Shutdown installed? 

If you have PowerChute Business Edition installed open a command prompt as an administrator and enter SC query apcpbeagent. If the query returns that APCPBEAgent State Stopped enter SC start apcpbeagent to start the service and then log in. 

If you have PowerChute Network Shutdown installed open a command prompt as an administrator and enter SC query pcns1. If the query returns that PCNS1 State Stopped enter SC start pcns1 to start the service and then log in. 

If in ether case if the system responds that the server does not exist then you should run the installer to install / update the PowerChute. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

Thanks so much for the detailed information.
I did the command prompt sequence, and it showed stopped. but when I tried to start it said denied.  I am logged in as admin, which is myself.
I think I'll have to uninstall and reinstall.
Business Powerchute business edition,   installed.  
-----
So I uninstalled and reinstalled.  And that worked.  My links sort of work, and gets me where to I can make settings.
I also installed the Console, but I'm thinking you also have to have the server setup to use the console, cause I couldn't log in with my user name I just made.
But at least I can get to the website now and check and make settings so I will have the shutdown when we have a power outage, which we do often here.
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore