Hello,
I hope you can assist me in my matter 🙏🏻
I have UPS with the following information:
Rack UPS 48 kW Symmetra PX2
it has dual IM with the following model on it tag: OG-SYMIM16
I have upgraded the firmware using (apc_hw05_aos722_sumx 722_bootmon109.exe)
the upgrade utility tools showed me error and that it is not compatible firmware and abort, while the IM took the firmware and I lost some components in the GUI like power modules and Dry contacts.
The old version information as below:
Model Number: 0G-9354A
Serial Number: QD1750111147
Hardware Revision: 0C
Manufacture Date: 12/14/2017
MAC Address: 28 29 86 01 98 F7
Management Uptime: 130 Days 8 Hours 45 Minutes
Network Management Card
---------------
Model Number: 0G-1236
Serial Number: 5A1750T32331
Hardware Revision: 05
Manufacture Date: 12/11/2017
Application Module
---------------
Name: px2
Version: v6.5.0
Date: Jul 20 2017
Time: 17:28:24
APC OS(AOS)
---------------
Name: aos
Version: v6.5.0
Date: Jun 9 2017
Time: 13:41:00
APC Boot Monitor
---------------
Name: bootmon
Version: v1.0.8
Date: Apr 8 2014
Time: 10:59:40
is there anyway I can fix this? please provide me with the latest suitable firmware for this UPS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-15 05:59 AM
The NMC firmware you loaded was for a Smart-UPS. You can simply download the correct Symmetra NMC firmware if this is a single phase unit.
If this is a three phase Symmetra unit you will need to contact APC Technical Support to obtain the same.
Be advised some NMC firmware now requires a subscription / paid license to obtain and install the firmware! 🤦♂️
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-22 06:33 AM
Thank you Teken for the reply, i was trying to solve it with technical support and they advise to upgrade to 7.0.4, but I'm unable to find that version anywhere. I hope they will provide it to me.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-23 02:12 PM
If they advised you to upgrade to v7.0.4 why would they not provide you the firmware directly or relay a resource link?!?! 🤔
If you receive a copy please do share the file as I’m sure it will help the next person asking the same. 👍