Where are the "app" .bin files?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Where are the "app" .bin files?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:24 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
7
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:24 AM . Last Modified: ‎2024-03-18 03:33 AM

Where are the "app" .bin files?

In the documentation and misc forum posts I've been reading, I've been seeing references to two .bin files -- the aos and app files -- though after downloading several firmware revisions, I've yet to see an App file included in the package. Where are these App files located?

I'm running an AP7901. Thanks in advance for any answers.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

In the documentation and misc forum posts I've been reading, I've been seeing references to two .bin files -- the aos and app files -- though after downloading several firmware revisions, I've yet to see an App file included in the package. Where are these App files located?

I'm running an AP7901. Thanks in advance for any answers.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:24 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:24 AM . Last Modified: ‎2024-03-18 03:33 AM

Thanks much for the reply!

The only file listed in FTP is apc_hw02_aos_116.bin -- no app file, which explains the status of "P+ N+ A-". APC support suggested I correct the issue by updating in steps starting with apc_hw02_aos227_rpdu220. Unfortunately, the bin files aren't being accepted via XMODEM. I'm connected at 96008N1, and XMODEM is using the same baud rate.

Once I start the transfer of the AOS bin, the log scrolls by too quickly for me to see what it's doing, then pauses here:

????????????[xmodem upload - Press CTRL-C to quit]?????????????
?Xmodem sectors/kbytes sent: 1/ 0kRetry 0: NAK on sector ?or
| Retry 0: Got 52 for sector ACK ?
?Retry 0: NAK on sector ?
?Retry 0: Got 20 for sector ACK ?
| Retry 0: NAK on sector ?-------
?Retry 0: Got 41 for sector ACK

Also, "About System" is showing two AOS installs, which is weird, because FTP only shows a single .bin.

-----------------------------------------------------------------------
Module Information

Description : Network Management Card AOS
-----------------------------------------------------------------------
Name : aos Type : APC OS
Version : 202 Sector : 39
Date : 12/29/2003 Time : 13:54:07
CRC16 : EDB9

Press to continue...

Description : Network Management Card AOS
-----------------------------------------------------------------------
Name : aos Type : APC OS
Version : 116 Sector : 63
Date : 02/07/2003 Time : 13:45:39
CRC16 : 9A88

Any advice?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:24 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:24 AM . Last Modified: ‎2024-03-18 03:33 AM

hi milkman,

if you are at AOS 1.x, you need to go to AOS 202 first, as outlined in the firmware upgrade instructions. AOS 202 is included with each firmware update.

can you no longer FTP to the card now? it may take some tinkering but here is some info. when you have an AOS and an APP on a card and upload the new AOS first, it overwrites the old APP on the card so briefly, you have two AOSs. the second file, the new APP, overwrites the old AOS, and thus you have a new AOS and new APP on the card.

it seems that you are stuck at the point with the new APP and AOS. what happens if you try via FTP?

by the way, do you have a case number from tech support? i am the tech support team leader on the product and would be glad to assist you over the phone since it can be a little difficult depending on what stage you're at.

if you want, i can email you and set up a time to chat unless you want to continue on the board but we may get to a resolution quicker while working on it, if you can while on the phone.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

Angela,

I would definitely appreciate the assistance. My incident ID is Incident: 100805-000857.

Are you available around 4:00pm CDT (in 1hr, 20 min)?

Greg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

i will send you an email to follow up

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

Just wanted to say a huge "THANK YOU" to i picKed a winna for assisting me with this issue. With her help, I was able to update the firmware and restore the app needed for DNS and Web access.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

glad to hear its all set. 8-)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1497
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

In the documentation and misc forum posts I've been reading, I've been seeing references to two .bin files -- the aos and app files -- though after downloading several firmware revisions, I've yet to see an App file included in the package. Where are these App files located?

I'm running an AP7901. Thanks in advance for any answers.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore