Mess: Power Wheeps and Extenders, something you should know

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Mess: Power Wheeps and Extenders, something you should know
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
6
1715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

Mess: Power Wheeps and Extenders, something you should know

I recently opened a post asking for the possibility of cutting APC power wheeps (http://forums.apc.com/spaces/6/racks-rack-accessories-cooling/forums/general/2836/understanding-pdu-...), I anticipated what the below pictures show.

There's no way you can make room for so many connectors to feed rack PDUs, not in a regular canalization. PDMs have a flawed design, they should bring a guaranteed hardwire connection. After all If you feel the need to change or replace some PDM it would be a major pain to free the wheeps through the whole installation.

Attachments
Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • afumex
  • hardwire
  • modular
  • PdM
  • pdu
  • power
  • wheep
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:26 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:26 AM . Last Modified: ‎2024-03-18 03:33 AM

I recently opened a post asking for the possibility of cutting APC power wheeps (http://forums.apc.com/spaces/6/racks-rack-accessories-cooling/forums/general/2836/understanding-pdu-...), I anticipated what the below pictures show.

There's no way you can make room for so many connectors to feed rack PDUs, not in a regular canalization. PDMs have a flawed design, they should bring a guaranteed hardwire connection. After all If you feel the need to change or replace some PDM it would be a major pain to free the wheeps through the whole installation.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

"come with breaker/whip moduels in various lengths"

This is not the case for 400v/230v configurations. PDPMs are all the same, what varies is the extender length (coming right of BOT).

Suppose in the future there where 400v/230V PDPMs with the desired lengths available without having to use extender wheeps,.. The whole point of a modular power distribution panel is being able to make changes, can you imagine removing one PDPMs 16Apms and replacing it by a 32Apms like the ones shown in the picture?

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

http://www.apc.com/products/family/index.cfm?id=431

The bottom of the list is all of the 400/230V breaker and whip modules with various lengths and current configurations from 140cm to 1080cm and you should be able to custom order 1680cm whips.

The number at the end of the part number is the length of the whip in CM.

Here is a PDPM that is unpopulated and you can order whatever breaker combination and length you choose to.

http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=PDPM277H

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

As i said before, the list is correct, but there are no combinations without extenders to match 32A and 16A monophasic circuits.
The only combinations available in the 32A range are:

32A
PDM1332IEC-3P
PDM1332IEC-3P-2
PDM1332IEC-3P-3

20A
PDM1320IEC-3P-1
PDM1320IEC-3P-2
PDM1320IEC-3P-3

16A
PDM1316IEC-3P

Message was edited by: fedelang

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

There is actually a pretty good reason the Breaker/whip module only has extenders available and not lenght to order.

The 400V/230V 5 wire whips are made to multiple lengths so that you can run the whip directly to the rack you want.

The 400V/230V 3X1 Breaker modules take the 3 single phases and run them each to a single phase connector. All the connectors should not be going to the same rack so you wouldn't want 3 single phase whips all the same length because you would end up with to much slack or not enough to reach the rack mount PDU so the correct thing to do in this case is to use a extender to reach each rack. If you are planning on running all three whips to the rack you would better off using 3 phase PDU's in the rack.

With this many whips and racks you would have been better off using 32A 3 phase rack mount PDU's and you could have avoided using the extenders and all of the mess.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:25 AM . Last Modified: ‎2024-03-18 03:33 AM

You are correct again, but not entirely. International part numbers for Rackmount PDUs are very limited in comparison with US RmPDU portfolio. There are no 7kW (equivalent to a 32A monophasic) three-phase pdus, you have to jump for 11kW PDUs or 22kW PDUs. And summing up thats why the solution with extenders is a pain.

BTW the solution came right out from APC ISX Configuration tool, with extenders included, and was approved that way by the staff despite my observations.

Even if APC could design a full range of whip sizes, the solution still fails for all non-standard datacenter layouts (most of them). Maybe next refresh could bring the Schneider Electric Powerclip technology to avoid this trouble.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:26 AM . Last Modified: ‎2024-03-18 03:33 AM

0 Likes
0
1715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:26 AM . Last Modified: ‎2024-03-18 03:33 AM

I recently opened a post asking for the possibility of cutting APC power wheeps (http://forums.apc.com/spaces/6/racks-rack-accessories-cooling/forums/general/2836/understanding-pdu-...), I anticipated what the below pictures show.

There's no way you can make room for so many connectors to feed rack PDUs, not in a regular canalization. PDMs have a flawed design, they should bring a guaranteed hardwire connection. After all If you feel the need to change or replace some PDM it would be a major pain to free the wheeps through the whole installation.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of