What type of UPS to put on a generator.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • What type of UPS to put on a generator.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-25 11:21 PM . Last Modified: ‎2024-03-19 03:10 AM

0 Likes
3
1322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 11:21 PM . Last Modified: ‎2024-03-19 03:10 AM

What type of UPS to put on a generator.

I have 4 UPS of the Back-UPS Pro type, when I switch on the power supply of my generator, these do not stop switching to mains battery, I have set their sensitivity to a minimum but this does not change nothing. The 4 UPS have the same problem and phenomenon.
By cons on the sector no problem
Could you tell me about the type of UPS that I could install, so that I no longer have this problem.
Thank you all

Labels
  • Labels:
  • Getting Started
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-25 11:21 PM . Last Modified: ‎2024-03-19 03:10 AM

0 Likes
0
1322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 11:21 PM . Last Modified: ‎2024-03-19 03:10 AM

On 1/3/2020 5:05 PM, Jean Luc said:

I have a GENYX G5000DT-2 generator.

From my limited searching it appears to be one of the more conventional rotating machines with AVR. The AVR tends to produce relatively awful mains waveforms on top of the fluctuating frequency. So you might be somewhat out of luck.

On 1/3/2020 5:05 PM, Jean Luc said:

I wonder if it was not possible to put a regulator at the outlet, in order to avoid the problem.

Can't think of anything that would work off the top of my head short of a full on-line UPS. I have no experience with the APC line of on-line UPS.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-25 11:21 PM . Last Modified: ‎2024-03-19 03:10 AM

0 Likes
0
1320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 11:21 PM . Last Modified: ‎2024-03-19 03:10 AM

It depends on what your generator is. If it's an inverter then you shouldn't have an issue. If it's a conventional rotating machine then you'll potentially have constant issues as minor load variations cause the frequency to walk around as the machine tries to govern its speed. You'll also see voltage variations per load.

Both of these conditions cause the UPS to see the mains as "outside tolerance" and will switch to and from battery as things move around. I've used a rotating machine and in inverter with my Smart-UPS(s) and  BackUPS, but had to make sure there was a fairly constant load on the rotating machine to keep the load stable.

Some cheaper conventional generators also have some "AVR" circuitry which can cause a distorted waveform while regulating the output voltage and there is almost no hope of getting those to work well with a UPS.

I love my little 3KVA Chinese inverter genny. It runs all the gear via 2 UPS (SU2200 & SUA3000), bot both switch to battery when I try and run the coffee machine at the same time due to the cycle controlled heater causing awful distortion of the mains waveform.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-25 11:21 PM . Last Modified: ‎2024-03-19 03:10 AM

0 Likes
0
1320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 11:21 PM . Last Modified: ‎2024-03-19 03:10 AM

Thank you for your reply.
This confirms my doubts, I have a GENYX G5000DT-2 generator.
I wonder if it was not possible to put a regulator at the outlet, in order to avoid the problem.
Or if it does not work, simply bypass the inverters on operation with the generator is also a solution.
thank you so much

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-25 11:21 PM . Last Modified: ‎2024-03-19 03:10 AM

0 Likes
0
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 11:21 PM . Last Modified: ‎2024-03-19 03:10 AM

On 1/3/2020 5:05 PM, Jean Luc said:

I have a GENYX G5000DT-2 generator.

From my limited searching it appears to be one of the more conventional rotating machines with AVR. The AVR tends to produce relatively awful mains waveforms on top of the fluctuating frequency. So you might be somewhat out of luck.

On 1/3/2020 5:05 PM, Jean Luc said:

I wonder if it was not possible to put a regulator at the outlet, in order to avoid the problem.

Can't think of anything that would work off the top of my head short of a full on-line UPS. I have no experience with the APC line of on-line UPS.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore