What settings for a graceful shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • What settings for a graceful shutdown
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:12 AM . Last Modified: ‎2024-03-06 01:58 AM

0 Likes
6
1728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:12 AM . Last Modified: ‎2024-03-06 01:58 AM

What settings for a graceful shutdown

Hi,
A couple of days ago I installed PowerChute V9 in Windows XP ProSP3 UPS is SUA1000I. Just have the Agent installed and login through FF.

Now, I was going through all the settings and help menu to try and figure out what was best for me. In fact I spent hours at it. Id made a couple of changes but cant remember what they are as we dad a 2 second power cut and my computer shutdown almost immediately. No time to close any programmes. Then the UPS turned off. Not what I call a graceful shutdown at all. 2 questions......

1/Is there anywhere or anyway I can find or get the default settings back? (please dont tell me to re-install)

2/ I am only using PowerChute on 1 workstation, though I have other things hooked up but not always running, connected to the UPS. I know I easily have at least 15 minutes with a full load on. Id like about 7 minutes before the computer is shut down. WHat settings do I use please?

Help appreciated thanks
Musical

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:13 AM . Last Modified: ‎2024-03-06 01:58 AM

0 Likes
0
1728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:13 AM . Last Modified: ‎2024-03-06 01:58 AM

Anyone?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:12 AM . Last Modified: ‎2024-03-06 01:58 AM

0 Likes
0
1728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:12 AM . Last Modified: ‎2024-03-06 01:58 AM

What does it take around here to actually get a resolution to your NOT UNREASONABLE question? What ? 4 or 5 days inbetween posts?

ANYONE???????

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:13 AM . Last Modified: ‎2024-03-06 01:58 AM

0 Likes
0
1728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:13 AM . Last Modified: ‎2024-03-06 01:58 AM

do you have the event log from when this happened so we can see the events recorded? how much total runtime does the software report with your load attached (versus the observed runtime of at least 15 minutes).

once we see the total amount of runtime and maybe look at the logs, i'd say we could make a good recommendation on how to configure things. i am not sure how to reset all the powerchute settings to default or if there even is a way to be honest.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:13 AM . Last Modified: ‎2024-03-06 01:58 AM

0 Likes
0
1728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:13 AM . Last Modified: ‎2024-03-06 01:58 AM

Thanks for your response. Heres is a cut and paste from the event log, with a little sample of the data log below ( I was playing around with the settings and only have some of that log, and as you will see the entries are only 10 secs apart.. )

At the moment with just my PC on, the runtime is 50 mins. Ive seen it at 60 with the same PC running. WHen I also have the Mac and some other associated low power- draw hardware turned on, the maximum load shows 3 Leds lit out of 5 on the UPS. The 15 mins is a conservative guess Ive taken from when I sized my ups for my needs when I purchased it. It is more like 20mins. I mostly shut my computers down when not in use or if Im out of the room and most of the time only one is going, thats why the load (in bold) shows a minimal reading here. Taking into account for when I have both computers on I still dont want to let it run on battery unnecessarily so I figure 7 to 10 mins is all I need, tops.

DO I have to have a command file operating to achieve this?


9/03/12 11:14:13 Communication Established
9/03/12 11:14:13 Monitoring Started
8/03/12 22:11:28 Monitoring Stopped
8/03/12 11:05:20 Communication Established
8/03/12 11:05:20 Monitoring Started
8/03/12 10:59:59 Monitoring Stopped
8/03/12 10:59:59 Monitoring Started
8/03/12 10:22:11 Monitoring Stopped
8/03/12 10:21:12 Power Restored
8/03/12 10:21:10 Shutdown process started
8/03/12 10:21:10 Power Failed
8/03/12 04:18:45 Communication Established
8/03/12 04:18:45 Monitoring Started
7/03/12 09:29:50 Monitoring Stopped
7/03/12 05:42:46 Communication Established
7/03/12 05:42:46 Monitoring Started
6/03/12 19:14:20 Monitoring Stopped
6/03/12 17:01:31 Communication Established
6/03/12 17:01:31 Monitoring Started
6/03/12 09:27:03 Communication Established
6/03/12 09:27:03 Monitoring Started
5/03/12 23:19:02 Monitoring Stopped
5/03/12 11:20:42 Communication Established
5/03/12 11:20:42 Monitoring Started
4/03/12 21:41:19 Monitoring Stopped
4/03/12 17:06:05 Communication Established
4/03/12 17:06:05 Monitoring Started
3/03/12 23:05:28 Monitoring Stopped
3/03/12 09:46:51 Communication Established
3/03/12 09:46:51 Monitoring Started
3/03/12 09:44:44 Monitoring Stopped
3/03/12 06:42:25 Communication Established
3/03/12 06:42:25 Monitoring Started


9/03/2012 16:12:17 N/A N/A 243.3 243.3 50 27.67 *24* 26.1
9/03/2012 16:12:07 N/A N/A 243.3 243.3 50 27.67 *23.4* 26.1
9/03/2012 16:11:57 N/A N/A 243.3 243.3 50 27.67 *27.9* 26.1
9/03/2012 16:11:47 N/A N/A 244.8 244.8 50 27.67 *27.9* 26.1


Musical

Message was edited by: Musical
Edited : to put the right column in boldface

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:13 AM . Last Modified: ‎2024-03-06 01:58 AM

0 Likes
0
1728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:13 AM . Last Modified: ‎2024-03-06 01:58 AM

i see you have a lot of monitoring started/stopped. you are monitoring via USB, correct? do you know why the communication is dropping? for instance, your computer going into hibernate and turning off USB?

what exactly would you like to accomplish - shut down the attached computer a few minutes after running on battery for the 7-10 minutes you mentioned?

what is the column you bolded? battery voltage or something else? i was thinking the column to the left of bolded was battery voltage but i am not sure without the column headings.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:13 AM . Last Modified: ‎2024-03-06 01:58 AM

0 Likes
0
1728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:13 AM . Last Modified: ‎2024-03-06 01:58 AM

Hi, thanks for your response.

Yes Im going thru USB. I have always shut my computer/s down when not in use, and if Im understanding correctly thats what youre seeing in the 1st log, or have I got that wrong? Sometimes I can boot up 3 times in a day. If my computer/s are idle and Im around the house and within earshot of the UPS, I'll leave things on for around 2 hours.

QUOTE:
"what exactly would you like to accomplish - shut down the attached computer a few minutes after running on battery for the 7-10 minutes you mentioned?"

Yes Id like PowerChute to gracefully shut down my XP computer AFTER running on battery about 7 mins so I can have more flexibility about going out of earshot. Once Ive achieved that then I need some explanation about how to shut down any programs that might be opened at the time as well, but 1st things 1st.

The bold is not voltage but load. I didnt initially paste in the headings coz they didnt display correctly but here they are in the correct order.

Date
Time
Min Line Voltage(VAC)
Max Line Voltage(VAC)
Input Line Voltage(VAC)
UPS Output Voltage(VAC)
Output Frequency(Hz)
Battery Voltage (VDC)
UPS Load (%)
Internal UPS Temp (°C)

Musical

Message was edited by: Musical to try and make my post clearer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:13 AM . Last Modified: ‎2024-03-06 01:58 AM

0 Likes
0
1729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:13 AM . Last Modified: ‎2024-03-06 01:58 AM

Anyone?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore