What happens when the power returns?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • What happens when the power returns?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

0 Likes
5
2289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

What happens when the power returns?

I am using PowerChute Network Shutdown. I have configured my servers to shutdown after the UPS has been on battery for 30 min. Assuming the servers have shut down gracefully, what happens when the power comes back on and load is returned? Will I have to manually turn my servers back on, or will they turn back on automatically?
Thanks,
Shain

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

0 Likes
0
2289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

Hi Shain,

how to configure 30 minutes on battery then shutdown the servers anyway ?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

0 Likes
0
2289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

I am using PowerChute Network Shutdown. I have configured my servers to shutdown after the UPS has been on battery for 30 min. Assuming the servers have shut down gracefully, what happens when the power comes back on and load is returned? Will I have to manually turn my servers back on, or will they turn back on automatically?
Thanks,
Shain

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

0 Likes
0
2289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

Shain,

There is a section on the network management card under UPS>Powerchute>Configuration called On-Battery Shutdown Behavior. If you enable Restart when power is restored, the UPS will power back on when it sees utility power again. Whether or not the server will restart depends on a setting in the BIOS. Here is a knowledgebase document that discusses the BIOS setting:

http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1003&p_created=1010390400&p...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

0 Likes
0
2289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

Thanks Grenade. One more related question. What happens here: UPS is on battery. At 30 min servers shut down per power chute. The UPS still has 30 more min of battery time remaining. At 45 min power is restored. Since load was never completely removed and restored, I assume that the servers will remain off?

Thanks,

Shain

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

0 Likes
0
2289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

In the PowerChute Network Shutdown Interface there is an option called "Turn off the UPS after the shutdown
finishes. (Not applicable to Silcon UPS)" in the "CONFIGURE SHUTDOWN" menu. If you check this box,
the UPS will start its sleep routine once the PowerChute agent has initiated its shutdown. In your example,
after 30 minutes, the PowerChute software would start shutting down followed by the UPS turning off. When
power came back at 45 minutes, the UPS would return online, and your server(s) should boot back up
depending on the BIOS settings.


This can become a bit more complicated if you have multiple servers that are set to shutdown at staggered
times. If this is the case, you will want to make sure that only the LAST server in your staggered shutdowns
has the "Turn off the UPS..." box checked. If the first server had that box checked, the UPS would go into
sleep mode sooner that you expected, and cause all the other servers to shutdown prematurely.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

0 Likes
0
2290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:51 AM . Last Modified: ‎2024-03-07 11:50 PM

Hi Shain,

how to configure 30 minutes on battery then shutdown the servers anyway ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore