Warmstart notification - SMART-UPS 6000 XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Warmstart notification - SMART-UPS 6000 XL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
connie.cook_apc
Ensign connie.cook_apc
Ensign

Posted: ‎2021-07-28 09:38 PM . Last Modified: ‎2024-02-14 02:33 AM

0 Likes
2
1552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:38 PM . Last Modified: ‎2024-02-14 02:33 AM

Warmstart notification - SMART-UPS 6000 XL

This morning, I received a notification that my UPS performed a warmstart. This is the first time this has happened and I have attempted to review the knowledgebase and other articles, but each time to click on the link to the support article, I am asked for the model of my UPS and then it just goes to the main support page. I have not been able to really read anything useful, so I must post in here to see if someone can assist me.

Here is some information regarding my unit:

11/19/2012 06:31:14 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Int Sensor at Int Sensor Loc) communication.
11/19/2012 06:30:23 UPS: Restored the local network management interface-to-UPS communication.
11/19/2012 06:25:33 UPS: Passed a self-test.
11/19/2012 06:25:17 UPS: Started a self-test.

Hardware Factory
Model Number: AP9619
Serial Number: NA0835009156
Hardware Revision: A10
Manufacture Date: 08/29/2008
MAC Address: 00 C0 B7 D2 91 D9
Management Uptime: 0 Days 3 Hours 52 Minutes
Application Module
Name: sumx
Version: v3.7.2
Date: 02/02/2010
Time: 19:08:16
APC OS (AOS)
Name: aos
Version: v3.7.3
Date: 02/02/2010
Time: 17:05:14

I've also attached my config.ini, event.txt and data.txt.

I would just like to be able to figure out what could have caused the warmstart and if there is a problem that I need to fix.

Many thanks!
Connie

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 6000_xl
  • smart-ups
  • warmstart
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
connie.cook_apc
Ensign connie.cook_apc
Ensign

Posted: ‎2021-07-28 09:38 PM . Last Modified: ‎2024-02-14 02:36 AM

0 Likes
0
1552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:38 PM . Last Modified: ‎2024-02-14 02:36 AM

Thank you very much. I appreciate the information.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-28 09:38 PM . Last Modified: ‎2024-01-31 02:56 AM

0 Likes
0
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:38 PM . Last Modified: ‎2024-01-31 02:56 AM

is this the site you were researching? http://www.apc.com/site/support/index.cfm/faq/

if not, please see if you can search for FA156063 there to review the knowledge base article on this topic.

looking at your logs, i would not be too concerned. it does not mean the UPS rebooted, only the network management card interface. the NMC generally does this as a failsafe to clear up any issues it might detect (i.e. if it cannot ping its default gateway). as long as it is not happening constantly/repeatedly, i would not worry.

Reply

Link copied. Please paste this link to share this article on your social media post.

connie.cook_apc
Ensign connie.cook_apc
Ensign

Posted: ‎2021-07-28 09:38 PM . Last Modified: ‎2024-02-14 02:36 AM

0 Likes
0
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-28 09:38 PM . Last Modified: ‎2024-02-14 02:36 AM

Thank you very much. I appreciate the information.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore