Virtualization Settings and VM Prioritization Setting Question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Virtualization Settings and VM Prioritization Setting Question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
135
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:49 AM . Last Modified: ‎2024-03-08 04:02 AM

0 Likes
3
1888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:49 AM . Last Modified: ‎2024-03-08 04:02 AM

Virtualization Settings and VM Prioritization Setting Question

I'm setting up a shutdown test for our servers with Powerchute Network Shutdown 4.3 in an advanced configuration. We have smart ups. The hosts are managed with Vcenter. I've setup the shutdown settings in Vcenter and left them at the default 120 seconds per VM shutdown. I have VM/vApp Shutdown selected. All of that makes sense to me until we reach the VM Prioritization Shutdown Duration and Groups timing. 

 

 Example:

  • 3 VM's set to shut down at 120 seconds per VM in Vcenter Guest Shutdown List.
  • VM/vApp Shutdown is Selected in Powerchute.
  • I have VM Prioritization turned ON in Powerchute.
  • Prioritize VM's:
    • I put 2 VM in Medium group.
    • I put 1 VM in High group.
  • VM Shutdown Duration:
    • Medium Group: 60 seconds
    • High Group: 120 seconds
    • The remaining groups are set to 0 seconds since they will not be used in this example. 

Does the group timing in VM Prioritization Shutdown Duration Settings need to match the shutdown timings for VM's in Vcenter Shutdown List? I'm trying to figure out whether my Vcenter Shutdown settings at 120 seconds actually matter when VM Prioritization is active? I think they do matter. But my brain is going in circles. In my head, if I did the example above. The shutdown procedure would fail because the Medium Group Duration is set to 60 seconds which is lower than Vcenters 120 second shutdown timing setting. The Medium Group would need to be set to 240 seconds since it has two VM's set to shutdown at 120 seconds per.  Am I correct in thinking that?  

 

 

Or does VM Prioritization completely over-ride Vcenter Shutdown List for guest shutdown timing?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:02 AM

0 Likes
0
1888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:02 AM

Hi,

Those setting in the user's guide refer to the setting needed when PCNS is configured with a standalone host. A standalone host is one that is not managed by vCenter or a hosts that the user has not configured PCNS to manage the VM/vApp shutdown. In you configuration the setting on the host would not be used since PCNS had already powered off the VMs. Since you have configured VM/vApp shutdown and priortized the VMs the recommendation is to disable those setting on the host. 

Sample shutdown process

1. NMC reports that the UPS is on battery.
2. Shutdown delay for the On Battery event elapses. PowerChute starts a maintenance mode task on each Host. At the same time it sends a command to turn off the UPS or Outlet Group if configured to do so.
3. PowerChute starts VM/vApp shutdown.
4. VM/vApp shutdown durations elapse and PowerChute gracefully shuts down the vCenter Server VM.
5. vCenter VM shutdown duration elapses.
6. PowerChute starts executing the shutdown
command file if configured to do so. 
7. Shutdown command file duration elapses.
PowerChute shuts down the VMware hosts
using the order on the Host Protection
page.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:49 AM . Last Modified: ‎2024-03-08 04:02 AM

0 Likes
0
1888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:49 AM . Last Modified: ‎2024-03-08 04:02 AM

Hi,

VM prioritization allow you to prioritize the order UPS shutdown and start up. The order for shutdown is un-prioritized VM power off first. Then group 2, group 1, low, medium and finally high priority VMs are power off. When starting up the order is reversed. High priority VMs first down to un-prioritize. Any priority group with set to a zero second delay is skipped. So, any VMs that are in a group that is set to zero will not be powered off or powered on. 

In your configuration the medium group will be powered off. PCNS will wait 60 seconds after issuing the command for the medium group to power off and then command the high priority group off. It will then wait 120 seconds and move on to the next step. If you have configured PCNS to shutdown vCenter server the default is 240 seconds so that would be the next step. After the 240 second vCenter shutdown delay elapse the host will be power off. 

Prioritization is explained start on page 43 of the user's guide https://download.schneider-electric.com/files?p_Doc_Ref=SPD_PMAR-9DNLQK_EN

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:02 AM

0 Likes
0
1888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:02 AM

Maybe I didn't ask my question right? You somehow answered everything that I already knew, but missed my question. Let me do it with pictures this time. Vcenter has it's own start up and shutdown setting for each host. This is where you would configure guest shutdown instead of hard powering down VM's. You can configure the hosts to shutdown in a specific order inside of Vcenter too. Page 18 of that user guide shows an example of using that and the pic is below. The default times in that example are also 120 seconds. Does Powerchute's VM Prioritization groups over-ride the internal Vcenter shutdown settings? So if I set the Virtual Machine Startup and Shutdown times in Vcenter to 120 seconds, and then went into Powerchute and set all of the groups to let's say 60 seconds. Which one has control of the shutdown process? VM Prioritization or Vcenter Startup/Shutdown Settings? DLgjoaDZSd9LiNrrsCuK5w%3D%3D.pngDLgjoaDZSd9LiNrrsCuK5w%3D%3D.png

Or have I misunderstood how this works?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:02 AM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:02 AM

Hi,

Those setting in the user's guide refer to the setting needed when PCNS is configured with a standalone host. A standalone host is one that is not managed by vCenter or a hosts that the user has not configured PCNS to manage the VM/vApp shutdown. In you configuration the setting on the host would not be used since PCNS had already powered off the VMs. Since you have configured VM/vApp shutdown and priortized the VMs the recommendation is to disable those setting on the host. 

Sample shutdown process

1. NMC reports that the UPS is on battery.
2. Shutdown delay for the On Battery event elapses. PowerChute starts a maintenance mode task on each Host. At the same time it sends a command to turn off the UPS or Outlet Group if configured to do so.
3. PowerChute starts VM/vApp shutdown.
4. VM/vApp shutdown durations elapse and PowerChute gracefully shuts down the vCenter Server VM.
5. vCenter VM shutdown duration elapses.
6. PowerChute starts executing the shutdown
command file if configured to do so. 
7. Shutdown command file duration elapses.
PowerChute shuts down the VMware hosts
using the order on the Host Protection
page.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore