VCSA fails to start after power outage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • VCSA fails to start after power outage
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:27 AM . Last Modified: ‎2024-02-15 12:18 AM

0 Likes
3
1411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:27 AM . Last Modified: ‎2024-02-15 12:18 AM

VCSA fails to start after power outage

I have successfully configured my two ESXi hosts to shutdown during a power outage. After numerous tests, I have noticed everything successfully shuts down but when powering up, PCNS fails to start the VCSA. The part that doesn't make sense is since PCNS can communicate with VCSA to start the shutdown sequence, how can it somehow forget where the appliance is located when its time to start it back up?

Here's my configuration:

ESXi Host 1 - x.139.4

VCSA and PCNS

ESXi Host 2 - x.139.7

Successfull VCSA settings:

ZFWt3ydoZj8rWPpiruCrQw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngZFWt3ydoZj8rWPpiruCrQw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Error.log of my last tests:

15-07-18 10:56:30,064 ERROR main com.apcc.pcns.configservice.ConfigurationService - === Starting PowerChute Network Shutdown ===

15-07-18 10:56:59,992 ERROR main com.apcc.pcns.SNMP.PcnsBaseAgent - SNMP Agent Engine ID:80:00:01:3e:01:7f:00:00:01:51:0d:e6:b8

15-07-18 10:57:32,355 ERROR Thread-2 com.apcc.m11.components.WebServer.util.virtualization.VMWareConnection - getVCenterServerConnection, Host 192.168.139.130 - . VI SDK invoke exception:java.net.NoRouteToHostException: No route to host

15-07-18 11:21:46,175 ERROR pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMWareConnection - Unable to connect to vCenter Host 192.168.139.130 - java.rmi.RemoteException: VI SDK invoke exception:java.net.SocketTimeoutException: connect timed out

15-07-18 11:21:49,181 ERROR pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMWareConnection - getVCenterServerConnection, Host 192.168.139.130 - . VI SDK invoke exception:java.net.NoRouteToHostException: No route to host

15-07-18 11:36:10,457 ERROR main com.apcc.pcns.configservice.ConfigurationService - === Starting PowerChute Network Shutdown ===

15-07-18 11:36:40,274 ERROR main com.apcc.pcns.SNMP.PcnsBaseAgent - SNMP Agent Engine ID:80:00:01:3e:01:7f:00:00:01:51:0d:e6:b8

15-07-18 11:37:12,466 ERROR Thread-2 com.apcc.m11.components.WebServer.util.virtualization.VMWareConnection - getVCenterServerConnection, Host 192.168.139.130 - . VI SDK invoke exception:java.net.NoRouteToHostException: No route to host

Host Protection:

zDxc%2FELZsuVHq3OMbeFLbw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngzDxc%2FELZsuVHq3OMbeFLbw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

I would like to remind that PCNS does everything is supposed to in the event of a power outage. The only issue is VCSA shuts down properly but just can't be restarted by PCNS when the hosts return online. 

P.S. Eventlog of my last test is attached. 

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:27 AM . Last Modified: ‎2024-02-15 12:18 AM

0 Likes
0
1410
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:27 AM . Last Modified: ‎2024-02-15 12:18 AM

Hi Lee,

1 - would you put PCNS into debug mode and run a shutdown and start up test and then attach the error.log, EventLog.txt and the pcnsconfig.ini file. Information on how to put PCNS into debug mode will be found in FAQ FA230514

2 - In your configuration do you have a vSAN configured?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:27 AM . Last Modified: ‎2024-02-15 12:18 AM

0 Likes
0
1410
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:27 AM . Last Modified: ‎2024-02-15 12:18 AM

Hi,

Are there any errors logged in the VCSA during the shutdown process?

The event log shows the host has come on-line is this based on you physically powering it on? 

Once the startup process has completed i.e. VMs on line and the VCSA remains off are there any entries remaining in the VirtualFileStoreProperties file?

Do you have the systems listed in a domain name server?

How many NIC are configured in host 139.4?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:27 AM . Last Modified: ‎2024-02-15 12:18 AM

0 Likes
0
1410
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:27 AM . Last Modified: ‎2024-02-15 12:18 AM

Hi,

Are there any errors logged in the VCSA during the shutdown process?

I don't see any errors in VCSA during the shutdown process. 

The event log shows the host has come on-line is this based on you physically powering it on? 

Yes. 

Once the startup process has completed i.e. VMs on line and the VCSA remains off are there any entries remaining in the VirtualFileStoreProperties file?

No, the file is empty. I made sure to check it. Unfortunately I don't remember if I did it before or after manually powering on the VCSA appliance. I could run another test if you'd like.

Do you have the systems listed in a domain name server?

No, I do not. Everything uses actual IP. 

How many NIC are configured in host 139.4?

Only one. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:27 AM . Last Modified: ‎2024-02-15 12:18 AM

0 Likes
0
1411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:27 AM . Last Modified: ‎2024-02-15 12:18 AM

Hi Lee,

1 - would you put PCNS into debug mode and run a shutdown and start up test and then attach the error.log, EventLog.txt and the pcnsconfig.ini file. Information on how to put PCNS into debug mode will be found in FAQ FA230514

2 - In your configuration do you have a vSAN configured?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of