Using a PDU mounting kit with a veritcal cable organizer
  • Using a PDU mounting kit with a veritcal cable organizer
Posted: ‎2021-06-28 03:15 AM . Last Modified: ‎2024-02-14 10:28 PM
724
My company is currently looking to add a couple of additional 4 post open racks (model # AR203). We would also like to use vertical PDU's (AP7830), which connects to a Symmetra LX 8kVA, instead of using horizontal PDU's. The horizontal PDU's would have to be mounted to the rear of the rack, and this would take up 1U of much needed rear space. Thus, I would like to use the PDU Mounting brackets (model # AR8415) in conjunction with the PDU adapter plate (AR8416).
I would also like to use a 3-in vertical cable organizer (AR8440A) that would be mounted between 2 of the racks; however, the veritcal cable organizer would need to be mounted on the rear of the racks. So, I am questioning on whether or not this will work. Does anyone know if the AR8415 PDU mounting brackets will impede mounting the vertical cable organizer if the two are mounted on the rear of the rack and on the same side?
  • ar203
  • ar8416
  • ar8440a
  • cable_organizer
  • mounting_bracket
  • pdu
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko
Hi Brian,
Sorry for the late response on this. I wasn't able to get to this until today.
The Cable organizer, like you said, should be installed between the two racks with no problems. The PDU's would be installed in the rear corner of the rack using the part #'s you mentioned, without a problem. I don't see from documentation and installation guides how this would not be capable of working together.
TheNotoriousKMP_apc
Sisko
Hi Brian,