Use ACRD200s as backup

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Use ACRD200s as backup
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:02 AM . Last Modified: ‎2024-03-18 11:43 PM

0 Likes
1
515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:02 AM . Last Modified: ‎2024-03-18 11:43 PM

Use ACRD200s as backup

We recently moved three ACRD200 (fluid cooled) units to a new data center that already has a cooling system. They are configured as a group, InRow mode. In our old data center, they were the primary cooling. In the new data center we'd like them to act as backups for when the primary cooling system fails. The primary system already keeps the room fairly cold (~72F without any trouble).

I have not been able to configure the setpoints so that the units do not run. Despite the cool setpoint being as high as 80-85, the units still cycle off and on. Are there any tips/tricks to accomplish this? I am aware of the risks of not running these units at all so we have a process in place to ensure they run once a week. Thanks!

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • cooling
  • inrow
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:02 AM . Last Modified: ‎2024-03-18 11:43 PM

0 Likes
0
515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:02 AM . Last Modified: ‎2024-03-18 11:43 PM

Tony,

Depending on which configuration type the units are set to, they will look at different temperatures to determine if cooling is needed.

Without knowing the exact layout/configuration, the best suggestion I can make is this.

Under Configure Group, set the units into Spot mode, with capacity control set to Discrete.  Then, set you cool setpoint to 78.8°F (the highest allowable), and set the Deadband to 10.0°F.  In this configuration, the units should not come on until the return air temperature reaches 88.8°F (your setpoint, plus your deadband).  The unit(s) will then continue to cool until the return air temperature gets down to 68.8°F (or, your cool setpoint, minus your deadband). 

This setting should, in most cases, allow the units to only come on during a failure of the primary cooling.

If you need further assistance, or want to discuss other configuration options, the best way to reach cooling technical support is calling in to 888-695-6500 and selecting the appropriate options.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:02 AM . Last Modified: ‎2024-03-18 11:43 PM

0 Likes
0
516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:02 AM . Last Modified: ‎2024-03-18 11:43 PM

Tony,

Depending on which configuration type the units are set to, they will look at different temperatures to determine if cooling is needed.

Without knowing the exact layout/configuration, the best suggestion I can make is this.

Under Configure Group, set the units into Spot mode, with capacity control set to Discrete.  Then, set you cool setpoint to 78.8°F (the highest allowable), and set the Deadband to 10.0°F.  In this configuration, the units should not come on until the return air temperature reaches 88.8°F (your setpoint, plus your deadband).  The unit(s) will then continue to cool until the return air temperature gets down to 68.8°F (or, your cool setpoint, minus your deadband). 

This setting should, in most cases, allow the units to only come on during a failure of the primary cooling.

If you need further assistance, or want to discuss other configuration options, the best way to reach cooling technical support is calling in to 888-695-6500 and selecting the appropriate options.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of