Use ACRD200s as backup

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
Enter a search word
    Turn off suggestions

    Didn't find what you were looking for? Explore advanced search

    Enter a search word
      Turn off suggestions

      Didn't find what you were looking for? Explore advanced search

      Enter a user name or rank
        Turn off suggestions

        Didn't find what you were looking for? Explore advanced search

        Enter a search word
          Turn off suggestions

          Didn't find what you were looking for? Explore advanced search

          Enter a search word
            Turn off suggestions

            Didn't find what you were looking for? Explore advanced search

            cancel
            Turn on suggestions
            Showing results for 
            Show  only  | Search instead for 
            Did you mean: 
            Important Note
            • Home
            • Schneider Electric Community
            • APC UPS, Critical Power, Cooling and Racks
            • APC UPS Data Center & Enterprise Solutions Forum
            • Re: Use ACRD200s as backup
            Options
            • Mark Topic as New
            • Mark Topic as Read
            • Float this Topic for Current User
            • Bookmark
            • Subscribe
            • Mute
            • Printer Friendly Page
            Invite a Co-worker
            Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
            You have entered an invalid email address. Please re-enter the email address.
            This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
            Please enter email address
            Send Invite Cancel
            Invitation Sent
            Your invitation was sent.Thanks for sharing Exchange with your co-worker.
            Send New Invite Close
            Top Experts
            User Count
            BillP
            Administrator BillP Administrator
            5060
            voidstar_apc
            Janeway voidstar_apc
            196
            Teken
            Spock Teken
            136
            Erasmus_apc
            Sisko Erasmus_apc
            112
            View All

            Free

            English

            Data Center Certified Associate Exam Development Path

            Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

            4.0
            Register Browse SE University

            Invite a Colleague

            Found this content useful? Share it with a Colleague!

            Invite a Colleague Invite
            Solved Go to Solution
            Back to APC UPS Data Center & Enterprise Solutions Forum
            Start a Topic
            Solved
            Anonymous user
            Not applicable

            Posted: ‎2021-06-28 12:02 AM . Last Modified: ‎2024-03-18 11:43 PM

            0 Likes
            1
            637
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-28 12:02 AM . Last Modified: ‎2024-03-18 11:43 PM

            Use ACRD200s as backup

            We recently moved three ACRD200 (fluid cooled) units to a new data center that already has a cooling system. They are configured as a group, InRow mode. In our old data center, they were the primary cooling. In the new data center we'd like them to act as backups for when the primary cooling system fails. The primary system already keeps the room fairly cold (~72F without any trouble).

            I have not been able to configure the setpoints so that the units do not run. Despite the cool setpoint being as high as 80-85, the units still cycle off and on. Are there any tips/tricks to accomplish this? I am aware of the risks of not running these units at all so we have a process in place to ensure they run once a week. Thanks!

            Labels
            • Labels:
            • Racks, Rack Accessories, & Cooling
            • Tags:
            • cooling
            • inrow

            Authentication Failed.

            • Authentication Ticket Mismatched, failed authentication.

            Link copied. Please paste this link to share this article on your social media post.

            • All forum topics
            • Previous Topic
            • Next Topic

            Accepted Solutions
            BillP
            Administrator BillP Administrator
            Administrator

            Posted: ‎2021-06-28 12:02 AM . Last Modified: ‎2024-03-18 11:43 PM

            0 Likes
            0
            637
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-28 12:02 AM . Last Modified: ‎2024-03-18 11:43 PM

            Tony,

            Depending on which configuration type the units are set to, they will look at different temperatures to determine if cooling is needed.

            Without knowing the exact layout/configuration, the best suggestion I can make is this.

            Under Configure Group, set the units into Spot mode, with capacity control set to Discrete.  Then, set you cool setpoint to 78.8°F (the highest allowable), and set the Deadband to 10.0°F.  In this configuration, the units should not come on until the return air temperature reaches 88.8°F (your setpoint, plus your deadband).  The unit(s) will then continue to cool until the return air temperature gets down to 68.8°F (or, your cool setpoint, minus your deadband). 

            This setting should, in most cases, allow the units to only come on during a failure of the primary cooling.

            If you need further assistance, or want to discuss other configuration options, the best way to reach cooling technical support is calling in to 888-695-6500 and selecting the appropriate options.

            See Answer In Context

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Reply 1
            BillP
            Administrator BillP Administrator
            Administrator

            Posted: ‎2021-06-28 12:02 AM . Last Modified: ‎2024-03-18 11:43 PM

            0 Likes
            0
            638
            • Mark as New
            • Bookmark
            • Subscribe
            • Mute
            • Permalink
            • Print
            • Email to a Friend
            • Report Inappropriate Content

            Link copied. Please paste this link to share this article on your social media post.

            Posted: ‎2021-06-28 12:02 AM . Last Modified: ‎2024-03-18 11:43 PM

            Tony,

            Depending on which configuration type the units are set to, they will look at different temperatures to determine if cooling is needed.

            Without knowing the exact layout/configuration, the best suggestion I can make is this.

            Under Configure Group, set the units into Spot mode, with capacity control set to Discrete.  Then, set you cool setpoint to 78.8°F (the highest allowable), and set the Deadband to 10.0°F.  In this configuration, the units should not come on until the return air temperature reaches 88.8°F (your setpoint, plus your deadband).  The unit(s) will then continue to cool until the return air temperature gets down to 68.8°F (or, your cool setpoint, minus your deadband). 

            This setting should, in most cases, allow the units to only come on during a failure of the primary cooling.

            If you need further assistance, or want to discuss other configuration options, the best way to reach cooling technical support is calling in to 888-695-6500 and selecting the appropriate options.

            Reply

            Link copied. Please paste this link to share this article on your social media post.

            Preview Exit Preview

            Photos

            • Upload Upload
            • URL URL
            • Saved Photos Saved Photos
            Upload location
            • Add Photos to Album:
            • New Album
            • Upload location
              • Add Photos to Album:
              • New Album
              Drag here to start uploading
              Drag photos here or
              Tap for upload options
              You must install or upgrade to the latest version of Adobe Flash Player before you can upload images.
            Photos

            never-displayed

            You must be signed in to add attachments

            never-displayed

             

            You’ve reached the end of your document

            WHAT’S NEXT?

            Ask our Experts

            Didn't find what you are looking for? Ask our experts!

            My Dashboard

            Check out the new Feeds and activities that are relevant to you.

            To The Top!

            Forums

            • APC UPS Data Center Backup Solutions
            • EcoStruxure IT
            • EcoStruxure Geo SCADA Expert
            • Metering & Power Quality
            • Schneider Electric Wiser

            Knowledge Center

            Events & webinars

            Ideas

            Blogs

            Get Started

            • Ask the Community
            • Community Guidelines
            • Community User Guide
            • How-To & Best Practice
            • Experts Leaderboard
            • Contact Support
            Brand-Logo
            Welcome to Schneider Electric Community!
            Forum-Icon

            You have two options to continue your visit.

            LOGIN / Register

            Why logging in?
            • You enable the complete set of features available, such as posting, sharing, subscribing, private messaging and more.
            • You unlock the access to the whole content that Schneider Electric Community has to offer, including the gated items and the special events.
            And it’s free of charge!!!

            OR

            Continue as a guest

            Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

            Welcome!

            Welcome to your new personalized space.

            of 1

            Explore
            Translating the page…
            The page is currently translating. Please wait.
            Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.