Urgent: Power Load

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Urgent: Power Load
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

0 Likes
6
1009
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

Urgent: Power Load

Hi Everyone,

How can I tell how much power the UPS device is using to power my devices? It see load percentages, however, my HVAC guys want to know how much VDC or VAC is being drawn.

Thank you,
D

Message was edited by: ddasilva99

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

3000 VA X 57.2% capacity = 1,710 VA
3000 VA X 63.9% capacity = 1,917 VA

The unit's themselves have a battery charger that is used when the battery has recently been used. The maximum the charger itself pulls is around 287 Watts. The unit operates at 120 VAC. This should be the information the electrician needs, but let me know if there is anything else.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

External batteries do not affect the amount of load drawn by the UPS, they simply provide more runtime during a power failure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

What is the VA capacity of the UPS and what is the load percentage being reported? This will tell us how much current in amps you are drawing from utility power. The AC voltage should remain the same regardless of the amount of devices being powered. It should be 120 VAC or 208 VAC depending on the feed to the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

I have two UPS systems:

2x- SU3000RMXL3U
6x- SU48R3XLBP

For each main unit (su3000) I have three external batteries connected (SU48). The load reported from UPS#1 is 57.2% and the load reported from UPS#2 is 63.9%

I hope this information helps.
D

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

0 Likes
0
1009
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

3000 VA X 57.2% capacity = 1,710 VA
3000 VA X 63.9% capacity = 1,917 VA

The unit's themselves have a battery charger that is used when the battery has recently been used. The maximum the charger itself pulls is around 287 Watts. The unit operates at 120 VAC. This should be the information the electrician needs, but let me know if there is anything else.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

Hi Grenade,

Does your numbers emcompass the three external batteries or without the three external batteries?

Thank you,
D

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

0 Likes
0
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:50 PM . Last Modified: ‎2024-03-15 02:55 AM

HVAC load is on APC site.
375.00 BTU/hr per unit.

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SU3000RMXL3U

The percent load on UPS is the watts. SU3000RMXL3U is scaled at 2.4kW = 100%, therefore with the values you provided, the connected loads totals 3kW, or 10250BTU (1kW x 3413 = BTU/hr). 10250 BTU + two x (375 BTU) =11,000

The UPSs + your current loads contribute to approximately 1-ton of load on the building HVAC system.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore