Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Updating different UPS' config.ini via iniutil.exe

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Updating different UPS' config.ini via iniutil.exe
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:54 PM . Last Modified: ‎2024-03-14 11:30 PM

0 Likes
3
2223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:54 PM . Last Modified: ‎2024-03-14 11:30 PM

Updating different UPS' config.ini via iniutil.exe

Hello,

Let me first present what I'm trying to do, and what the steps I have taken to accomplish my goal:

I need to update a total of 14 UPS' so that Warning & Critical events have a delay of 5 minutes on their notifications (changed from default of 2 minutes)

When I log into individual UPS' via the web, and attempt to change the delay for entire groups of events, the way the interface works, I need to enable all of the subevents in that group - this forces me to go back and edit individual single groups and single events back to the way they were.

I'd like to get a little more granular with my edits, so I looked to the config.ini and was hoping to make some edits there. Here's my problem (well, two really):

1. I can't download a config.ini from the Smart-UPS 700 series APC's - do these have config.inis?

2. On the other APC's I have been able to download the config.ini from (2200s), I don't see the event notification delay setting (looking for the default setting of 2 - and would like to bump it up to 5)

Here's the closest thing I could find, and this doesn't look right:

TAPCarrier3DataBits=7
TAPCarrier4DataBits=7
MessageDelay=0 seconds
Repeat=1 try
PageInterval=1 minute
NumericSiteID=""
SiteName=APC Management
SiteIDMode=IP address



Lastly, does anyone have any best practices for making small changes to multiples of UPS? Do you save individual config.inis and edit those? How does multiple UPS updating work? When I download a file from a given UPS, it's the individual config.ini, with no distinguishing characteristics to the filename.. so if I were to try and upload to multiple UPS', they would all pull the information from a single config.ini?

Any help would be most appreciated!

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:54 PM . Last Modified: ‎2024-03-14 11:29 PM

0 Likes
0
2222
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:54 PM . Last Modified: ‎2024-03-14 11:29 PM

let me try to help..

1.) AP9606 management cards do not have config.ini files. network management cards AP9617, AP9618, and AP9619 only have config.ini files in 2.5.0 firmware.

2.) the delays for the events are located at the bottom of a config.ini. it is really card to set these up via the config.ini in my opinion but here is what the configuration looks like for this particular event with the default settings, the e-mail will be repeated every 2 minutes, until the condition is cleared.

; UPS: The output power is turned off.
E0114=ES,E[+-05S+02M-1:::],T[:::::],P[:::]

i would personally configure one the way you like it, then download the config.ini file (you can download just the event configuration portion of it) then push that section out to the rest of the cards you want to.

the bits you posted from the config.ini file is from the paging section of the card.

[this may help too in regards to mass configuration|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8979]

[this may also answer a couple questions|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=9376]

let me know if this info helps or if i missed something.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:54 PM . Last Modified: ‎2024-03-14 11:29 PM

0 Likes
0
2222
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:54 PM . Last Modified: ‎2024-03-14 11:29 PM

I Picked a Winna,

The first link you supplied explains exactly what I was looking for - thanks much!

Regarding the older NMC's (AP9606s) - is it possible to change the notification delay? If so, how can I do that?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:54 PM . Last Modified: ‎2024-03-14 11:29 PM

0 Likes
0
2221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:54 PM . Last Modified: ‎2024-03-14 11:29 PM

no, unfortunately not. only AP9617, AP9618 and AP9619 have it on firmware 3.x.

AP9606 (all firmware versions) and AP9617/18/19 1.x and 2.x firmware versions do not have the ability to customize event delays, etc

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:54 PM . Last Modified: ‎2024-03-14 11:29 PM

0 Likes
0
2223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:54 PM . Last Modified: ‎2024-03-14 11:29 PM

let me try to help..

1.) AP9606 management cards do not have config.ini files. network management cards AP9617, AP9618, and AP9619 only have config.ini files in 2.5.0 firmware.

2.) the delays for the events are located at the bottom of a config.ini. it is really card to set these up via the config.ini in my opinion but here is what the configuration looks like for this particular event with the default settings, the e-mail will be repeated every 2 minutes, until the condition is cleared.

; UPS: The output power is turned off.
E0114=ES,E[+-05S+02M-1:::],T[:::::],P[:::]

i would personally configure one the way you like it, then download the config.ini file (you can download just the event configuration portion of it) then push that section out to the rest of the cards you want to.

the bits you posted from the config.ini file is from the paging section of the card.

[this may help too in regards to mass configuration|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8979]

[this may also answer a couple questions|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=9376]

let me know if this info helps or if i missed something.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of