Posted: 2021-06-28 11:23 PM . Last Modified: 2024-03-14 02:54 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:23 PM . Last Modified: 2024-03-14 02:54 AM
Firmware is 3.5.8. UPS model : 3kva Smart UPS
Customer set Bypass Upper Voltage at 265V and when the incoming voltage is 255V, the output voltage is set to 240V they received a ‘UPS: Bypass not in range; high voltage’ alert.
Any ideas why this would occur as it appears that with the Upper Voltage set to 265 an input of 255 should not generate an alert?
I asked for and got input voltage data from a little before 12/10/2009 21:15:10 to a little after 12/11/2009 04:00:29
I can send this if required
Date Time Vmin Vmax Vout Iout % Wout %out FrqOut %Cap Vbat
12/11/2009 04:02:54 249.78 252.38 240.27 2.28 22.61 18.36 49.96 100.00 217.75
12/11/2009 03:02:53 253.36 255.30 240.19 2.34 23.48 19.00 49.99 100.00 217.81
12/10/2009 21:12:52 250.58 253.64 240.33 2.75 27.20 22.13 49.98 100.00 217.72
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:23 PM . Last Modified: 2024-03-14 02:54 AM
Is this an international model in an international config? I noticed the output frequency is 50hz rather than 60. Do you have the exact model number of the UPS?
Also, in regard to the message, is that the exact error - it specified high voltage as the cause? Was this an email alert or reported in the NMC web interface?
Finally, we recently released v3.7.1 for the card's firmware, and an update couldn't hurt.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:23 PM . Last Modified: 2024-03-14 02:54 AM
The UPS can continue to operate with the input voltage it is getting. However the message you are getting is probably a result of the bypass voltage being to much of a difference from the UPS output to make an uninterupted transfer from UPS to Bypass.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:23 PM . Last Modified: 2024-03-14 02:54 AM
Is this an international model in an international config? I noticed the output frequency is 50hz rather than 60. Do you have the exact model number of the UPS?
Also, in regard to the message, is that the exact error - it specified high voltage as the cause? Was this an email alert or reported in the NMC web interface?
Finally, we recently released v3.7.1 for the card's firmware, and an update couldn't hurt.
Link copied. Please paste this link to share this article on your social media post.