Posted: 2021-07-09 04:18 AM . Last Modified: 2024-02-14 11:05 PM
Dear Forum,
When i try to attemp the PDU device it appear the error below:
I can login to PDU via telnet as showed below
Compared with another device ( PDU) that is ok ( i can login via web) it seem to be the same and Ok.
Can you please advice me?
PS: i have some important equipament connected to this PDU.
I appreciate your help
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:18 AM . Last Modified: 2024-02-14 11:04 PM
You should upgrade all of your units that have 6.0.9 firmware on them as soon as possible, as shown in your screenshot. Please read this information bulletin on why -> http://www.apc.com/us/en/faqs/FA237061
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:18 AM . Last Modified: 2024-02-14 11:04 PM
Hello,
This error can happen when the firmware application does not load properly. It looks like you're a few revisions behind the current release revision of rPDU firmware - I would recommend starting with a firmware upgrade (which can be done while the PDU is in production). You can get the latest rev of FW here: http://www.apc.com/us/en/tools/download/download.cfm?sw_sku=SFRPDU2G644&software_id=MFOI-ADJJT2&fami...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:18 AM . Last Modified: 2024-02-14 11:04 PM
You should upgrade all of your units that have 6.0.9 firmware on them as soon as possible, as shown in your screenshot. Please read this information bulletin on why -> http://www.apc.com/us/en/faqs/FA237061