Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-30 02:09 AM . Last Modified: 2024-03-11 12:13 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:09 AM . Last Modified: 2024-03-11 12:13 AM
I am setting up radius authentication on our rack PDU's and I am able to log in using radius but it is only logging my account in as Read Only and not admin. I am using Network Policy Server for Radius authentication. I also created a network policy with the vendor specific information listed below.
Vendor Code - 318
Checked Yes it conforms
Vendor assigned attribute number - 1
Attribute format - Decimal
Attribute value - 1
Any help would be greatly appreciated.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:10 AM . Last Modified: 2024-03-11 12:13 AM
Hi Nate,
Have you set the "service type" attribute to "Administrative"? I believe it might default to "login" which is read only.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:10 AM . Last Modified: 2024-03-11 12:13 AM
Hi Nate,
Have you set the "service type" attribute to "Administrative"? I believe it might default to "login" which is read only.